Can someone confirm please - I don't think this will make any difference but - would the replacement of a B Type breaker for a D Type have any effect on whether a compressor/motor start-up dimmed the lights in an installation? (assuming that both MCB's were able to cope with the current demands)
Thanks
 
Can someone confirm please - I don't think this will make any difference but - would the replacement of a B Type breaker for a D Type have any effect on whether a compressor/motor start-up dimmed the lights in an installation? (assuming that both MCB's were able to cope with the current demands)
Thanks
But your Zs certainly would....
 
agree with glennspark. changing from a b type to a d type, will mean that the MCB will require 20x In to disconnect instaneously. This means that your Zs values need to be a lot lower in order to alow for this.

Zs= Ipf/Uo
 
Last edited:
What's Zs (or maximum allowed) got to do with dimming lights on start up?

nothing at all, was just an observation that the max. Zs would decrease id a type d were to be fitted. and be4 you say it, neither did my post about turkey have anything to do with it, except that the lights thewre are always dim. a bit like me after as skinfull
 
nothing at all, was just an observation that the max. Zs would decrease id a type d were to be fitted. and be4 you say it, neither did my post about turkey have anything to do with it, except that the lights thewre are always dim. a bit like me after as skinfull

Point Taken. Always thought big birds and booze don't mix though.
 

Reply to D Type MCB's in the Australia area at ElectriciansForums.net

Similar Threads

  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
Replies
15
Views
1K
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K
There is no requirement to install RCD protection to PV system AC cable unless it's required because of installation method as mentioned above, or...
Replies
2
Views
3K
  • Question
Yeah, I've now got all that but with the electronic timer. The ABB AF contactors aren't compatible with the Schneider SD timer, but ABB don't do a...
Replies
17
Views
3K
Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2
Replies
42
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks