I have read various methods of daisy chaining downlighters and I was wondering which you guys think are the pros and cons of each.

Taking for example a JCC GU10 fitting. It says the terminals are suitable for loop in - loop out and they certainly seem big enough but the manufacturers instructions also state that heat resistant rubber or silicone flex should be used.

The ways of doing this I can see are:
1. 1.5mm2 T+E loop in and out of the fitting directly. But obviously this goes against the manufacturers instructions as there is no heat resistant cable in proximity to the fitting and there is a risk of melted cable.
2. 1.5mm2 T+E loop in and out of an ashley J501 or similar with a stub of Heat Resistant flex to the fitting. Seems like a good plan but introduces even more screw terminals with short stubs of T+E between each box. What were the manufacturers intentions in putting a connector big enough for loop in loop out if this is what is required?

Given that the light output from the downlighters means they normally need to be placed within say 1m of each other is there any reason you couldn't go with:
3. Ashley J501 as a junction box for the switch and incomming supply with the output to the first downlighter in 1.0mm2 heat resistant flex and then daisy chain all the fittings together with more 1.0mm2 heat resistant flex?
 

Reply to Daisy chaining of downlighters in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top