I have a customer who lives in a grand old house which suffers from damp.

The ground floor sockets (2 different circuits) IR test at around 0.3Mohms L/N-E. This was actually 0.01Mohms but I have already done some fault finding and managed to improve it.

Most of the back boxes are very rusted and flaking to bits with moisture inside them. As stated, I have done some improvements to the sockets and boxes but this has only managed to get the IR up to 0.3Mohms (L/N-E). I have looked thoroughly for any more sockets/FCU's that I may have missed but I now feel the remaining fault(s) are within the walls, even though this doesn't make sense as I can't see how moisture would have got inside the cable (Its black/red metric PVC).

I think the existing cables have metal capping within the damp walls, but again, even if this capping is rusting I cant see how it will affect the PVC covered cable. The wiring is approx 25 years old

My questions are..

1. What can you do about damp? It's pointless to rewire as the damp problem will still be there. Are there ways to protect the boxes and sockets from damp?

2. What are the solutions if I cannot raise the IR above 0.3Mohms? I'm guessing I have to map out the entire circuit, and find every single fault, but then what? It's an immaculate house, surface trunking not an option, new cable in wall not really an option as existing damp problem already somehow affecting cables in walls (unless some kind of cable joints in walls which are affected).

3. Are these designed to be installed in the wall? 2 Gang 35mm PVC Flush Box Round Corners with 20mm Conduit KO White (Sold in 1's) - https://www.cef.co.uk/catalogue/products/1063228-2-gang-35mm-pvc-flush-pattress-box-round-corners-with-20mm-conduit-ko-white

Usually fault finding is easy. 1 fault, bit of IR testing, fix fault. In this case there are faults everywhere and not just in the actual sockets!
 
Last edited:
OK gentlemen and ladys just sold a house and this that I did having a bad damp.
1) chip all the plaster off 1mtr high
Spray walls with salt remover
2) inject a damp proof between the bricks two course high
3) slurry the walls with sbr
4) mix render with sbr
5 top coat with finish plaster
6) wait till 6 months paint walls after.
that's good. should just about last till the buyer's cheque clears. 🤣🤣🤣
 
Friend of mine has house which he has owned for years. Lived in it initially then rented it out after that. Old terrace with solid walls and concrete floor. I've lost count of what he's spent on damp proof injection, cement rendering, removing floor and laying damp proof membrane etc. Mostly done by professional people. House still has damp issues now.
 
Most of the damp is tracking a cross from one wall to the other, where debris betwen the bricks. And need clearing out
And a problem on a bay window taken the render off in side and hoover all the crap out, I bet one on here will say why did I not remove the bricks out side, answer accie bricks.
 
I have a customer who lives in a grand old house which suffers from damp.

The ground floor sockets (2 different circuits) IR test at around 0.3Mohms L/N-E. This was actually 0.01Mohms but I have already done some fault finding and managed to improve it.

Most of the back boxes are very rusted and flaking to bits with moisture inside them. As stated, I have done some improvements to the sockets and boxes but this has only managed to get the IR up to 0.3Mohms (L/N-E). I have looked thoroughly for any more sockets/FCU's that I may have missed but I now feel the remaining fault(s) are within the walls, even though this doesn't make sense as I can't see how moisture would have got inside the cable (Its black/red metric PVC).

I think the existing cables have metal capping within the damp walls, but again, even if this capping is rusting I cant see how it will affect the PVC covered cable. The wiring is approx 25 years old

My questions are..

1. What can you do about damp? It's pointless to rewire as the damp problem will still be there. Are there ways to protect the boxes and sockets from damp?

2. What are the solutions if I cannot raise the IR above 0.3Mohms? I'm guessing I have to map out the entire circuit, and find every single fault, but then what? It's an immaculate house, surface trunking not an option, new cable in wall not really an option as existing damp problem already somehow affecting cables in walls (unless some kind of cable joints in walls which are affected).

3. Are these designed to be installed in the wall? 2 Gang 35mm PVC Flush Box Round Corners with 20mm Conduit KO White (Sold in 1's) - https://www.cef.co.uk/catalogue/products/1063228-2-gang-35mm-pvc-flush-pattress-box-round-corners-with-20mm-conduit-ko-white

Usually fault finding is easy. 1 fault, bit of IR testing, fix fault. In this case there are faults everywhere and not just in the actual sockets!
Hello HippyHappyDad. This will be a tough one to find. The cables themselves will not be the problem - they work ok in damp environments. As above, remove every fitting you can find, dry the cable ends and test individually. My suspicion would be buried choc bar connectors plastered directly into a damp wall and hidden from view; kitchen fitters occasionally perform this trick when a kitchen gets re-modelled. If the wall has been re-plastered, only the householder's knowledge might help with identifying the location of any redundant accessory that was removed. Sometimes moving the sockets up to 4ft above floor level gets them out of the damp zone. Sometimes, a surface box is better than a flush one for a damp wall. Possibly a nail in the wall has gone into a cable (the RCD should trip for this). All a bit of a PITA. Regards,
Colin Jenkins.
 
Hello HippyHappyDad. This will be a tough one to find. The cables themselves will not be the problem - they work ok in damp environments. As above, remove every fitting you can find, dry the cable ends and test individually. My suspicion would be buried choc bar connectors plastered directly into a damp wall and hidden from view; kitchen fitters occasionally perform this trick when a kitchen gets re-modelled. If the wall has been re-plastered, only the householder's knowledge might help with identifying the location of any redundant accessory that was removed. Sometimes moving the sockets up to 4ft above floor level gets them out of the damp zone. Sometimes, a surface box is better than a flush one for a damp wall. Possibly a nail in the wall has gone into a cable (the RCD should trip for this). All a bit of a PITA. Regards,
Colin Jenkins.
Thanks for that Colin.
A very decent reply for your 2nd ever post 😊.
I think removing all fittings and testing is unfortunately the way forward.
 
I did a job for an old doctor's office turned into a manse decades ago, it had some form of electrolytic/osmotic damp protection. No idea if / how it worked but walls were dry with no visible signs of damp ingress
 

Reply to Damp problems in sockets... solutions? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

I am living in the north of Thailand outside of the big city. That means in the rainy season we have multiple times per week power outages...
Replies
0
Views
459

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top