As per the text again in the real world of electrical work which I have been doing for 30 years you do have to work on a live fuse board now and again and anyone who has worked In a commercial or school environment will agree or just lie to go along with the people who " have never worked on anything live".. And yes to answer your question it does now mean that if I have to replace one of these items I will have to rethink how I go about this..
This is the reason I never post on these sites because I was trying to give a heads up to anyone who might be in a situation where they are replacing one I didn't want them to receive a shock like I did. But unfortunately most people on this site prefer to be argumentative and pick on the isolation side rather than actually pass on some info that might help someone..
 
Has anyone installed the new compact rcbo from crabtree and noticed a flaw that they have introduced that doesn't exist on the older larger model starbreaker rcbo..
The basics of it are that the new compact rcbo when plugged into the busbar in a circumstance that many will come across where you can't turn off the mains once the rcbo is clicked in but still in the off position the neutral tail actually bacomes live and has upto 170 volts on it, therefor if u touch this and then the neutral bar you become part of the circuit and get a shock..
It sounds to me as though you have uncovered a design fault. The internal trip mechanism must be fed from the live side of the breaker , not the protected side. Quite rightly you would not expect the neutral tail to be "live" when the circuit breaker is off.
 
WE can go on about live working, until the cows come home.
Simple fact is, an RCBO is a means of isolation.
This particular RCBO is not doing what it should be doing.
If I were to isolate the circuit protected by this RCBO to swap over a damaged socket front, the Neutral would be live as would every other Neutral connected to the Neutral bar.
Only if the neutral is disconnected at mains
 
could this be a similar scenario to a circuit that has L energised with a load in circuit, and the N floating (dissed). due to the no current flow = 0 V drop, the N is sitting at 230V. this disappears when N is connected. in the RCBO case, the load would be the internal gubbins in the RCBO.?????
 
could this be a similar scenario to a circuit that has L energised with a load in circuit, and the N floating (dissed). due to the no current flow = 0 V drop, the N is sitting at 230V. this disappears when N is connected. in the RCBO case, the load would be the internal gubbins in the RCBO.?????
Yes think that is exactly what is happening just that you don't normally think of your rcbo as a load but more of a disconnection device that if its switched off u wouldn't expect anything to be live..
 
Yes think that is exactly what is happening just that you don't normally think of your rcbo as a load but more of a disconnection device that if its switched off u wouldn't expect anything to be live..
An isolator only isolates the outgoing terminals. The fly lead is an incoming terminal.
If you turn off an isolator it only isolates the outgoing terminals. the incoming line terminal is certainly of course still at phase voltage, and if there is any circuitry the incoming neutral would be live too if parted. If it's not parted it would be close to installation earth voltage.

This example can repeat in other situations so do take care - imagine a Usb double socket or similar. If you switch the socket off and leave the line connected and part the neutrals somewhere, you'd expect to get a shock from the neutral.
All current carrying conductors are to be treated as live for this reason, including neutral.

Glad you're ok and thanks for the reminder of the risks.
 
An isolator only isolates the outgoing terminals. The fly lead is an incoming terminal.
If you turn off an isolator it only isolates the outgoing terminals. the incoming line terminal is certainly of course still at phase voltage, and if there is any circuitry the incoming neutral would be live too if parted. If it's not parted it would be close to installation earth voltage.

This example can repeat in other situations so do take care - imagine a Usb double socket or similar. If you switch the socket off and leave the line connected and part the neutrals somewhere, you'd expect to get a shock from the neutral.
All current carrying conductors are to be treated as live for this reason, including neutral.

Glad you're ok and thanks for the reminder of the risks.
 
yeah i just noticed :oops:
Yes page 3 I think.. Not really into the electronics side so all too much for me but don't like it when people go from a blue wire to a white wire and back to blue again.. Makes u wonder if its all wired correctly as it should be as like I said the old style rcbo didn't have this problem.. Can probably take some more pictures if anyone wanted..
 
I also got a tingle off a reduced height RCBO fly lead before Christmas (think it was a Hager but it could have been a Crabtree, can't remember which) . Didn't think much into at the time because I was in a massive hurry...
It stands to reason that all RCBOs made this way will have the same issue.
 
I realize this post is over a year old but I have some info that may clear this up. Don't know if anyone will see this now but I thought I'd post it anyway.
I recently had the same issue getting a light shock off the neutral flylead.
After looking up the specs of this RCBO I found the reason.
They claim 2 things about it. 1/ That is is double pole. 2/ You can IR test the circuit with the breaker off.
This can only mean that the electronics are on the supply side and not the load side. Hence, when connected to the busbar the flylead becomes live.
The leaflet that comes with it says to isolate the busbar but as has been pointed out, this is the real world and EAWR does allow live working. Irrespective of that they should have labeled the RCBO clearly that the flylead becomes live on connection and the electronics are on the supply side. A circuit diagram on the side is not enough.
The claim is that you don't have to disconnect conductors to do an IR test. I would rather do that than have this situation. One poster said that you can connect the flylead first which is exactly what I did on the others that I instaledl. However, you shouldn't have to do it that way as how do you dress it in round the other wires without a great deal of hassle.
This had been dangerously designed for one simple reason. Any experienced spark knowing how RCBOs work would not expect the electronics to be on the supply side.
Another thing. What if there was a problem with the electronics itself. You wouldn't be able to turn it off without isolating the whole board and removing it.
Very poorly thought out, and for what? Being able to IR test without removing conductors.
Next they'll be making them with four terminals so you can ring continuity test without removing conductors.
 
I realize this post is over a year old but I have some info that may clear this up. Don't know if anyone will see this now but I thought I'd post it anyway.
I recently had the same issue getting a light shock off the neutral flylead.
After looking up the specs of this RCBO I found the reason.
They claim 2 things about it. 1/ That is is double pole. 2/ You can IR test the circuit with the breaker off.
This can only mean that the electronics are on the supply side and not the load side. Hence, when connected to the busbar the flylead becomes live.
The leaflet that comes with it says to isolate the busbar but as has been pointed out, this is the real world and EAWR does allow live working. Irrespective of that they should have labeled the RCBO clearly that the flylead becomes live on connection and the electronics are on the supply side. A circuit diagram on the side is not enough.
The claim is that you don't have to disconnect conductors to do an IR test. I would rather do that than have this situation. One poster said that you can connect the flylead first which is exactly what I did on the others that I instaledl. However, you shouldn't have to do it that way as how do you dress it in round the other wires without a great deal of hassle.
This had been dangerously designed for one simple reason. Any experienced spark knowing how RCBOs work would not expect the electronics to be on the supply side.
Another thing. What if there was a problem with the electronics itself. You wouldn't be able to turn it off without isolating the whole board and removing it.
Very poorly thought out, and for what? Being able to IR test without removing conductors.
Next they'll be making them with four terminals so you can ring continuity test without removing conductors.
Thanks freelec for the update on this, I had nearly forgotten about this but shouldn't have as the amount of worry over working live this thread caused kept me replying for a while .lol??
 

Reply to Dangerous upgrade to crabtree rcbo's in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
6K
suffolkspark
S
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
V
  • Question
The installation was complete.There are 2 other lighting breakers on the other side of the CU which is out of camera shot.They are not RCD...
Replies
10
Views
3K
Videodoctor
V
V
How long had it been like it. I remember doing a test on a property many years ago and the earthing conductor, in my opinion had never been...
Replies
1
Views
2K
C
Looks like a haphazard attempt at TN-C, where the PEN conductor goes all the way to the end. Not necessarily the best and not familiar to us in...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks