H
Hawk
Got called to a job to investigate smoke coming from an industrial single phase socket. Met with the client and he said there was a bang, sparks and smoke coming from the socket. He showed me to it and I started investigating. The circuit was still live so I isolated it and noticed the circuit was fed from a 50A type D mcb. The circuit was feeding a forklift charger which was rated at 44A, however the cable supplying the socket was only 6mm and the length of run was around 30mtrs! The cable was completely melted. See picture attached. I made safe the circuit and left it isolated so it can not be turned on until I get back to upgrade the cable.
I was wondering why the circuit didn't trip if the live and earth touched, which I assume due to the sparks and a bang that was seen and heard. I haven't carried out any tests yet although I was getting 230v between live and earth. I take it the disconnection times have not been met?
I was wondering why the circuit didn't trip if the live and earth touched, which I assume due to the sparks and a bang that was seen and heard. I haven't carried out any tests yet although I was getting 230v between live and earth. I take it the disconnection times have not been met?