im doing inspection on flats and ive came across
all 61900 type c rcbo ive recommended changing to type b
due to type c for inductive loads . could cause overload
what is the general opinon on type c on domestic?
 
Hey Scott.

I'm a little confused by your post mate, a C type merely copes better with a high start-up current than a B type, and as it's an RCBO the breaker type isn't really an issue.

I believe wylex and crabtree only make their RCBO's in C type.

Can you elaborate on your "could cause overload" statement please.

Cheers
 
Last edited by a moderator:
I take it you mean 61009?

As long as your Zs is within the lower limits of a type C then i dont see a problem at all.

In fact, some manufacturers dont even make B type RCBO's.
 
Last edited by a moderator:
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.
 
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.

Our house has just been rewired by southern electric, with all type c rcbo's and nic'ed... Ther's nothing wrong with type c breakers so-long as the zs is still met..
 
I wonder why they do that Dan, Agree with the zs part, but i would bet that the majority of domestic premises are type b, don,t you think.

I also agree with you that the majority of domestic are on type b breakers, but really does it matter type b or c?, i don't really think it matters, and as far as a danger - well, i dont think so ...
 
Chaps,

The MAJORITY of manufacturers do not even make B type RCBO's as there is no real reason to.

The C type covers all installations, provided that the EFLI is within the maximum permitted. (or 80% corrected)
 
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.

hi there

type c are used a lot in some lighting appilcations such as display lighting, air con etc but they are also used to give a bit more before all the lovely 3 kw fan heaters are connected in the office when the heating breaksdown lol:rolleyes:

cheers
 
Hi

Am I reading this correctly?

Page 44 OSG table 7.1.

On a ring circuit for a TNS system, No RCD, 2.5/1.5 T+E
A "type C rcbo" is not permitted ZS being the prohibitive factor?

Thanks
 
Its not a case of needing one its a case that some manufacturers dont do b types so it would be useful if a c type was permitted.......

for instance I am doing a kitchen and the location of the CU makes it desirable to put in a RFC just for the kitchen..the previous electrician decided to put in a 16th split board and put the only ring and both lighting circuits on the rcd side. (niceic registered and told the customer he had done it to 17th regs????) so all lights and power on same rcd....I thought one solution would be to put kitchen ring on uprotected side on rcbo, but board is wylex and the b types rcbo's are hard to get hold of
and as discussed it appears that c types are not permitted for this type of circuit:confused:
 
You will also notice that it does not permit C type MCB's either although this is mainly for TNS systems.

Im trying to find info in the BRB with regards to this.

It just doesnt seem right to me.



Well looking in the BRB it gives EFLI values for type C MCB's and RCBO's so im not really sure what the OSG is on about.
 
Last edited by a moderator:
Your right Jason it does give ELI figures, although they are low, but still if your readings are less then I don't see the problem either?? maybe someone can thro some light on this as the OSG says that the prohibitive factor is the Zs???????
 
Hi,
Just bought 3x Wylex type B RCBO's online from Gil-Lec. Previously I contacted Wylex (via Electrium online) to find out if they still manufacture type B's and they replied that they do.

Hope this is helpful.
 
One good thing about type c rcbo or mcb in a domestic lighting circuit because of it's higher tolerance doesn't always trip when a lamp blows.
As for the zs cos it's a rcbo the maximum allowed shoots up to 1666 ohms and if your measurements are that high debating between type b and c would be the last thing on my mind!
 

Reply to dangers on type c for domestic help in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
820
  • Question
Single Pole, Single Pole Switched Neutral, and Double Pole are all different things. Hager RCBO's are Single Pole. I was recommending Single Pole...
Replies
33
Views
5K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
  • Question
Before you retire doing sparking will will be a halhoolick ask Tele. Lol.
Replies
7
Views
3K
Hi, My probe was on the outgoing neutral of the RCBO. I will be testing again this week so I will play around, many thanks for your reply.
Replies
7
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks