dangers on type c for domestic help

S

scott g

im doing inspection on flats and ive came across
all 61900 type c rcbo ive recommended changing to type b
due to type c for inductive loads . could cause overload
what is the general opinon on type c on domestic?
 
Hey Scott.

I'm a little confused by your post mate, a C type merely copes better with a high start-up current than a B type, and as it's an RCBO the breaker type isn't really an issue.

I believe wylex and crabtree only make their RCBO's in C type.

Can you elaborate on your "could cause overload" statement please.

Cheers
 
Last edited by a moderator:
I take it you mean 61009?

As long as your Zs is within the lower limits of a type C then i dont see a problem at all.

In fact, some manufacturers dont even make B type RCBO's.
 
Last edited by a moderator:
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.
 
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.

Our house has just been rewired by southern electric, with all type c rcbo's and nic'ed... Ther's nothing wrong with type c breakers so-long as the zs is still met..
 
I wonder why they do that Dan, Agree with the zs part, but i would bet that the majority of domestic premises are type b, don,t you think.

I also agree with you that the majority of domestic are on type b breakers, but really does it matter type b or c?, i don't really think it matters, and as far as a danger - well, i dont think so ...
 
i think for all of us who understand that type c have half the max permitted eli of a type b it doesnt matter, but not everyone realises this and that is where the risk is,( know your max eli and all is well)
 
Chaps,

The MAJORITY of manufacturers do not even make B type RCBO's as there is no real reason to.

The C type covers all installations, provided that the EFLI is within the maximum permitted. (or 80% corrected)
 
We only use C type when we are dealing with machinery or motors, due to the higher start up current being drawn for that split second, not heard of em in domestic situation unless they have made a boo boo.

hi there

type c are used a lot in some lighting appilcations such as display lighting, air con etc but they are also used to give a bit more before all the lovely 3 kw fan heaters are connected in the office when the heating breaksdown lol:rolleyes:

cheers
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
scott g,
Last reply from
scotsparky,
Replies
24
Views
16,917

Advert

Back
Top