Just your thoughts on this DB,it’s a Lewden type,I personally don’t like them.
Bus bar,not ideal,main switch on right,space very tight to make connections,hate the rcbo’s,screws in front of each other,making it hard to retighten .

[ElectriciansForums.net] DB installed connected & tested
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
You are literally talking milli seconds before the upfront RCD trips aswell as the RCBO. what's the installation method of the distribution circuit feeding the loxone?
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
Yeah but even when the downstream RCBO trips the N-E fault will still remain and therefore will trip the main RCD after the time delay because the RCBO will only disconnect the line of the CCT the neutral and earth are still in the bars and the fault will be seen by the RCD main switch. IMHO the best way to sort it and achieve discrimination is to change the MCB to an RCBO and have an upfront isolator rather than a main switch.
 
Yeah but even when the downstream RCBO trips the N-E fault will still remain and therefore will trip the main RCD after the time delay because the RCBO will only disconnect the line of the CCT the neutral and earth are still in the bars and the fault will be seen by the RCD main switch. IMHO the best way to sort it and achieve discrimination is to change the MCB to an RCBO and have an upfront isolator rather than a main switch.
Yea I can see where everyone is coming from,we are talking about a n/e fault here,I know it’s on aTT system,but realistically
These faults may be happening all the time,on most earthing systems,with negligible currents flowing.
N/e faults have always been a pain,& so be it if all power is disconnected,also if the rcbo disconnects that circuit surely that prevents any fault being on that circuit ie:N/E.,no current will flow to Earth ,arguing the fact the rcbo will trip on a N/E fault.
This is getting mighty confusing.
 
Ok,if the fault happens on the 30ma protected circuits,theses would trip before the time delay Rcd.
That’s why the time delay Rcd is installed.
It’s no-different set up than the above literature supplied by the manufacturers.
I can see your points about the N/E scenario,thinking that would be the worst case.
When this set up was introduced years ago,it worked well,preventing complete disconnection, of power.
Yeah but even when the downstream RCBO trips the N-E fault will still remain and therefore will trip the main RCD after the time delay because the RCBO will only disconnect the line of the CCT the neutral and earth are still in the bars and the fault will be seen by the RCD main switch. IMHO the best way to sort it and achieve discrimination is to change the MCB to an RCBO and have an upfront isolator rather than a main switch.
Yea I can see where everyone is coming from,we are talking about a n/e fault here,I know it’s on aTT system,but realistically
These faults may be happening all the time,on most earthing systems,with negligible currents flowing.
N/e faults have always been a pain,& so be it if all power is disconnected,also if the rcbo disconnects that circuit surely that prevents any fault being on that circuit ie:N/E.,no current will flow to Earth ,arguing the fact the rcbo will trip on a N/E fault.
This is getting mighty confusing.
even with no current flowing the act of joining the N and earth will trip the rcd try it on a dual rcd board switch off the mcb for say a socket circuit and short N-E the RCD will trip so it makes no difference if the RCBO trips in that board it will still trip the upfront RCD it isn’t compliant with BS7671 if you haven’t achieved discrimination in all fault conditions of final circuits and should be noted as a departure on the EIC along with an attached risk Assessment
 
That applies to all time delay DB’s.If the mcb is changed to a rcbo,then a main switch installed,IMO,that’s makes it worse,N/E remains.
But it will still only trip the affected CCT the fault will remain until rectified but the the circuit will not be able to be energised which should mean that no dangerous current should flow from nuetral to earth
 
My issue with the Lewden boards is the advised torque settings, I have two torque drivers and with either if I torque them to manufacturers settings it has a tendency to damage the rcbo screws.
Never had a torque driver...and never had a problem.
We should go back to double screwed terminals.....it'd give everybody two chances of getting at least one right. Like these, maybe. :cool:
[ElectriciansForums.net] DB installed connected & tested
 
Never had a torque driver...and never had a problem.
We should go back to double screwed terminals.....it'd give everybody two chances of getting at least one right. Like these, maybe. :cool:
View attachment 42407
Gotta love the old Wylex boards :D actually I think Wylex are returning to double screws for the tails anyway
 

Reply to DB installed connected & tested in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
500

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top