Evening and happy Friday!

Does anyone regularly use or know of a suitable way to relocate a DB from its original position (adjacent to main fuse) if there is nowhere within 3m of the main fuse inside the building where a fused isolator can be fitted?

Main fuse is in an external meter cabinet, current DB position is on the other side of the wall, new DB position is to be 10+ metres away.

Is there a surface mounted external box which can be fitted in which a fused isolator can be installed inside?

Is there another way of fitting it internally which is still acceptable?

Thanks.
 
You can usually squeeze a KMF into the meter box
 
There are 2 x meter setups inside the meter cabinet so no room for much else!

Looking like a external surface mounted meter cupboard could be the way forward.

Any harm in drilling through the back of the meter cabinet and through the wall, then bringing the tails through the wall, into trunking taking them up into a suspended ceiling and fitting the 80/100A fused switch up there?

Would need to be a decent sized metal switch though to take a 25mm SWA away me thinks.
 
There are 2 x meter setups inside the meter cabinet so no room for much else!

Looking like a external surface mounted meter cupboard could be the way forward.

Any harm in drilling through the back of the meter cabinet and through the wall, then bringing the tails through the wall, into trunking taking them up into a suspended ceiling and fitting the 80/100A fused switch up there?

Would need to be a decent sized metal switch though to take a 25mm SWA away me thinks.
why SWA if in trunking?
 
if tails are> 3m then fusing down to 80A makes sense, protecting the DNO fuse. have you opened it to check that it is what it says on the tin?
 
I usually drop the downstream OCPD to 63A for a 100A main fuse. I think 80A is too close to ensure that this will blow first. I thought there was something in the regs about this, but I can't find it with a quick flick through... maybe someone with a soft copy can find it ?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Newcastle Upon Tyne
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
DB to be located away from DNO equipment
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24
Unsolved
--

Advert

Thread statistics

Created
IAmSparkytus!,
Last reply from
bigspark17,
Replies
24
Views
3,987

Advert

TrueNAS JBOD Storage Server

Back
Top