All,

I have had a battery back up unit installed for warehouse lighting for the emergency lighting.
It has stopped working and the investigation was found to be a short circuit that affected the unit.
However after being informed by the designer that both the positive and negative connections would've needed to touch the casing (earth) but unless I am having a mind blank only the positive would require to touch the casing (earth) to take a chunk out of the casing and short? Under the other circumstance when it was being installed if the connections were on the battery and one of them touched the casing this would also cause a short?

As I wasn't around for the installation and have been landed with this I would appreciate all the input available.

I feel as if I am having a mind blank and hopefully I am not.

regards,
 
Both positive and negative of the battery are needed to connect the battery via the metal casing. There is no connection to earth for the battery on either pole so there is not a circuit when one pole of the battery touches an earthed piece of metal.
If the battery system had one pole earthed to the LV system earthing (not a good idea) then the other pole touching and earthed conductor would cause a short.

[ElectriciansForums.net] DC battery back up units
 

Reply to DC battery back up units in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
948

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
good thinking ps electrics i'll run with that. thanks
2 3
Replies
33
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top