I was asked earlier this week to look at a solar system on an office/warehouse that had stopped working (not my install). The strings all come into a Fronius DC box on the roof. When I opened it up it was pretty clear why the system had stopped producing:

[ElectriciansForums.net] DC fuse blowout

I'm looking for opinions on what may have caused this so it won't happen again. Why are 3 of the sets of fuses blown but not the fourth? Could lightning have been involved, or was it something more mundane?
 
Direct, or induced, surge most likely I'd imagine. I can't imagine that the fuses were rated incorrectly. Any Type2 or Type1 devices fitted to the DC circuit on the array-side of the combiner box? Was the array frame earthed/bonded to the MET? Any damage to the inverters?
 
Thanks for the reply SiberSolar. I still have some investigating to do, but what I know so far: There are no SPDs fitted between the arrays and the box. The panels are spread out in three lots on a metal roof, with nothing earthed back to the MET. The inverters don't appear to be damaged, but I haven't fully tested them yet.
 
Anything that can be done to prevent it, assuming it was caused by lightning? Would having the array earthed back to the MET help to prevent a blow out like this?
 
erm, is that 4mm2 cable used as the link from the fused combiners?

fuse combiners that look to be combining 5 circuits, each running at say 8 amps = 40amps running through a single 4mm2 cable continuously for hours on end.

Assuming that this is a system with standard mono / poly panels and not something like solar frontier thin films, then the answer to the question is incompetence (I assume it's clear what I'm getting at).

Also probably not tightened fully on the burned out sections would be why they burned out rather than the left hand neutral combiner.
 
Could be a loose connection overheating. I've seen this before on normal electrical circuits and the heat seems to spread to connections close by.
 

Reply to DC fuse blowout in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
410
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top