DC or AC breaker | on ElectriciansForums
Discuss DC or AC breaker in the UK Electrical Forum area at ElectriciansForums.net
Leb
Hi everyone,
I need your assistance to determine whether the breaker in the attached image is a DC breaker and whether there is a sign indicating that it is for the DC side and not the AC side.
[ElectriciansForums.net] DC or AC breaker
The fact it is 3 pole, suggests it is intended for 3ph ac.
Most dc breakers are single or double pole.
It only lists 50/60hz in its rating table
So I would not consider it suitable for DC.
Reply to DC or AC breaker in the UK Electrical Forum area at ElectriciansForums.net
Thanks Westward, and that last paragraph with the Note about no characteristic marking is exactly what I needed to see.
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Use wago connectors instead, much easier and safer I think
Given the apparent lack of earth, combined with no short circuit or over current protection, I'd contend that luck has been the sole factor...
nicebutdim
N
What you're trying to do here is break the first and second laws of thermodynamics which, of course, is impossible. There are always losses in a...
    • Optimistic