Evening all I'm looking at a machine which has a B&R HMI 24v not working,
The usual display is replaced with a page saying a product code needs entering and the touch screen is not responsive,
So it looks like we will be replacing it as it's under warranty still.

However after talking to different operators each with varying versions it transpires that there was a backup generator test yesterday

There's 2 identical machines, both not turned off at the time, and according to one guy they couldn't restart this one

Another said it wasn't used again as no product required

Another says it ran perfectly but took longer to reboot than usual and started fine this morning

All sounds a bit fishy

I would think a DC power supply would just shut down or have internal protection for devices downstream

Is it a possible this could have caused the HMI to develop a problem?
 
It is a make of plc that i avoid wherever possible, in my experience, they have a failure rate far higher than others that i have used.

It is possible for a power supply to fail and damage down stream equipment, when ever i have come across similar things in the past, it has often been the case that a 230v power supply has been used between phase and neutral, a momentary or prolonged failure of the N can destroy the PSU, a 3 phase psu or 400 to 230v transformer normally prevents such issues from re occuring.
 
Sorry I forgot to say the power supply is still functioning there is 24v present

So maybe the question should be
can there be issues caused downstream while the Psu is not damaged by an event?

Re B&R
I had never heard of B&R Plc's before moving to this company ( still relatively new to this )and we do have issues on this particular machine where questions have been put to B&R about glitches in the IO and they admitted they were aware of it and don't know what is causing it
 
it is sounding like a power surge or similar has either corrupted the memory or somehow put the device into shipping mode where a code is required by the commissioning engineer to make it work.

unfortunately the best people to give you advice are B&R,
however i have found there sales team about as scrupulous as a double glazing salesman
and there after sales team about as useful as a box of chicken nuggets at a vegans convention.
 
Ok so it is feasible that a surge could have left the Psu intact but affected devices it powers

I would hope my company will have decent cooperation from B&R as they spend a very large amount of money to them each year

Thanks for your input James!
 
Remember, some spikes, surges, transients, (same "poo" different words) can come down the earth cable destroying devices connected also to "real earth" or phase/N cables.
 
Ok so it is feasible that a surge could have left the Psu intact but affected devices it powers

In my own experience this is vanishingly rare as far as incoming voltage transients and brownouts giving rise to out-of-spec DC output are concerned. I run hundreds of DC PSUs on dodgy power from all sorts of generators, inverters etc, feeding studio equipment, and I am not aware of any downstream damage ever having been caused. I have had probably 50 or more PSUs blown up by 400V but nothing downstream was affected. I have seen adverse power events cause circulating ground currents to blow signal interconnects open, where equipment on different power sources is interconnected with single-ended signals. But if this panel is in the machine or fed from it, that seems improbable.

Therefore if there was a link to the genny test, it is more likely to be that the equipment or PSU had not been turned off for a long time and there was a brownout that triggered a latent problem that would have shown up as soon as the next restart occurred. This I have had many times - something appears to be working fine and you power-cycle it either intentionally or accidentally while doing some maintenance, and it does not come back up. You assume it's something you did, but it's actually an issue that has been lying in wait for years.
 
In my own experience this is vanishingly rare as far as incoming voltage transients and brownouts giving rise to out-of-spec DC output are concerned. I run hundreds of DC PSUs on dodgy power from all sorts of generators, inverters etc, feeding studio equipment, and I am not aware of any downstream damage ever having been caused. I have had probably 50 or more PSUs blown up by 400V but nothing downstream was affected. I have seen adverse power events cause circulating ground currents to blow signal interconnects open, where equipment on different power sources is interconnected with single-ended signals. But if this panel is in the machine or fed from it, that seems improbable.

Therefore if there was a link to the genny test, it is more likely to be that the equipment or PSU had not been turned off for a long time and there was a brownout that triggered a latent problem that would have shown up as soon as the next restart occurred. This I have had many times - something appears to be working fine and you power-cycle it either intentionally or accidentally while doing some maintenance, and it does not come back up. You assume it's something you did, but it's actually an issue that has been lying in wait for years.

The curse of the switch-mode power supply - capacitors dry out and you only become aware if ever the power fails. A place where I used to work had a really old pabx system which nobody ever dare power off in case it never came back on.
 
Or sometimes the start-up bootstrap resistor, the high value one that trickles a bit of rectified mains into the SMPSU control supply reservoir cap to get it running long enough to provide its own hot-side ELV rail. Often something like 100kΩ 1W; if they have skimped and used carbon film instead of metal, it's more likely to be open

I have a story about a rather high-profile piece of kit that went haywire when it was power-cycled for the first time in years. About half of its fifty 12V 1kW power supplies did not restart, and it took weeks and a high 5-figure bottom line before it worked properly again. I won't clutter the thread up with that though.
 
Psu is still functioning and the HMI is around 4 mths old as there were some software issues on the old version and a new version was installed into a HMI and sent over during 1st lockdown
So maybe an underlying problem with the device as suggested

The machines are left on all the time as keeping the panel warm helps with reducing condensation building up inside, it's a machine which washes a reusable plastic tray for food industry so lots of water and the panel is on top if the processing section

I've seen a much older one recently where a customer has rebuilt a complete panel away from the machine as the panel components were disintegrating from moisture getting in through damaged/ missing seals.

Generally the operator can reset the machine or power off and reboot if nothing else works so they tend to be left on.

However there are approx 500 of these machines globally, and I've been told this is the first time they've seen this problem
 

Reply to DC power supply and generator in the Electrical Engineering Chat area at ElectriciansForums.net

Search Electricans Forums by Tags

Tags Cloud - Most Used Words - Use them to search for topics

110v 12v 17th 17th edition 18th 18th edition 2 way 2330 2365 2391 240v 3 phase 6mm access account across adding additional advice advise after again alarm alarms always am2 amendment amp another answer anybody anyone anything appliance appliances application apply apprentice apprenticeship approved area arial armoured around assesment assessment attach aus ausie elec available basic bathroom batteries battery because become becoming becsa before being bell best better between black block blowing board boards boiler bonding book books bosch box boxes brand breaker breakers british bs7671 bsi build builder building bulb bulbs business button c&g cable cable size cables calculation calibration camera can't canada car caravan card career cctv ceiling central central heating cert certificate certificates certification certs certsure change changes changing charge charger charging cheap check cheers christmas circuit circuits clamp class code codes college combi coming commercial companies company competent complete condition conductor conductors conduit confused connect connected connecting connection connections connector connectors consumer consumer unit contact contactor content continuity contract contractor control controller conversion cooker copper core correct cost council couple course courses cover cpc cps crabtree cupboard current customer customers dead deal degrees demand design details detector device dewalt diagram difference different dimmer dimmer switch dimmers distribution diversity diy dno doing domestic domestic installer don't door double downlight downlighters downlights drill driver earth earth rod earthing east economy economy 7 ecs edition eic eicr elecsa electric electrical electrical installation electrical nvq electrical tools electrical wiring electrical work electrician electricians electricians london electricians mate electricians vans electricity electrics electriians mnchester element email emergency emergency lighting employed energy engineer engineering enough entry equipment essex every everyone exam existing experience extending extension external extra extractor extractor fan fan fans fault fault finding faulty fcu final finding fire fire alarm first fit fitted fitting fittings fixed flat flats flex flickering floor fluke fluorescent for sale forms forums found free fuse fused fused spur fuses garage garden gas generator get getting going great green grid ground gu10 guidance guide guilds hager halogen happy having heat heater heaters heating hello help help please help! hi everyone hnc hob home honeywell hot tub hours house how to ideas immersion impedance improver in london incoming induction industrial industry information infraction inside inspection inspection and testing install installation installations installed installer installers installing insulated insulation insulation resistance insurance interesting intro introduction inverter inverters isolation isolator issue issues jib jib card job jobs joining junction keeps kewtech kit kitchen knowledge lamp lamps large lead leads leakage led length lenny level level 2 level 3 light light switch lighting lighting circuit lights little live load local location loft london long looking looking for work loop low voltage ltd machine main main switch mains maintenance makita manchester manual mate max maximum mcb mcbs mcs media megger member members message metal meter meter tails meters method metrel mft might minor missing mobile module money motor mounted mounting moving multi multifunction multiple murdoch myself napit need help needed needs neutral never new new build new member newbie niceic night no earth north not uk not working notifiable number nvq off offer office old online opinions options other out outbuilding outdoor outlet outlets output outside oven overload panel panels parallel part part p passed pat pat testing people periodic person pfc phase phone pipe pir place plan plastic plate please plug plumbing advice pme point points pole position possible post posts power practical practice price prices pricing private problem problems project property protected protection protective pump pvc qualification qualifications qualified quality query question questions quick quote radial range rated rates rating rcbo rcbo's rcbos rcd rcd tripping rcd's rcds reading readings really recommend recommendations red regarding registered regs regulations relay remote repair replace replacement replacing required requirements resistance results rewire right ring ring final ring main roman roof room rose running safe safety salary sale saying scheme scotland screwfix sds second section security self self employed sensor series service services shed shock short shower simple single single phase site plan size sizing skills sky small smart smoke smoke alarms socket sockets software solar solar panel solar pv someone something sorry source south spark sparks sparky split spur spurs standard start starter starting steel still storage storage heater strange strip students stuff sub main suggestions supplier suppliers supplies supply supply to surge swa switch switched switches switching system systems t&e table tails taking terminal termostat test tested tester testers testing tests thank the forum their thermal thermostat these thing things thinking those though thought thoughts thread three three phase through time timer times tips today too tool tools trade trainee training transformer transformers trip tripped tripping trips trunking trying tt system type under underfloor underfloor heating unit units update upgrade urgent used using value values valve van vehicle video volt drop voltage voltage drop volts wall wanted warning water weeks welcome west what's whats where white wind wire wired wireless wires wiring wiring help within without work working works worth wrong wylex years zone zones

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top