Amp David

-
Mentor
Arms
Joined
Oct 2, 2009
Messages
5,115
Reaction score
911
Location
Glossop
Does anyone bother de rating XLPE 90 deg C max CCC to PVC 70 deg C max CCC, when connecting to accessories rated at 70 deg max?

Only reason I ask is this week I was given very strange looks when I pointed out that some 16mm XLPE clipped direct would require a 63 amp fuse and not 80 like they had in place.

Is it me just taking the actually regs to seriously are something?
 
Cheers, good to know i'm not going mad.

Seen it on more than 1 occasion where its already been installed and pointed it out, but nothings been done to sort.
 
Not wanting to

View attachment 8077

But this has always struck me as an odd situation. We now have a cable type of a higher temperature rating than the termination devices. It all seems a bit out of kilter to me. OK the cable will cope with higher ambient temperatures along the run, but it’s still got to terminate somewhere and copper being what it is heat will travel along it.
I may be totally off course with this but I’m curious (as the bishop said to the actress).
 
When rating higher temp cables it clearly states that the what you attach the cable too has to be able to take the higher temp.

I am glad I read this thread, I would never have thought to de-rate, but will from now on!
 
how do we know, without a lot of research , what temperature terminals etc. will withstand without deterioration. OK, their spec. will state that they are capable of running at 70deg. C, as that has always been ( generally speaking ) the max. temp. of cable. who's to say they won't happliy run at 90deg.C without corresponding with manufacturers?
 
To be honest we tend to oversize cables for actual demand in the smaller sizes anyway, and the larger sizes of cable are terminated to switchfuses, DB's, ect, which I bet are rated to 90deg anyway. Obviously this is not confirmed, and should always be checked.
 
Id have a read of REG 523.

If the accessories are not adequately rated then the cable will need derating.

Manufactures specify the temp limits for there equipment, some are less than 70C. As stated above its probably prudent to design to a max of 60 - 65 degrees where possible.

Regards Chris

Regards Chris
 

Reply to De rating of XLPE SWA cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
123
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
Sounds more positive.
Replies
8
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top