Just had a call off my electrician (one doing council work)

He did a CU change - on testing he IR tested the lighting circuit (500v DC) and got acceptable readings.
When he energized the circuit - RCD trips. Found a dead short between N and E. Investigating now to locate which run of cable/accessory is providing this dead short now. There are no Low Voltage equipment on lighting so nothing could of been damaged.

Any ideas what could of caused this?
 
But what we don't understand was when he IR tested between N&E there was no fault >900Mohms = good reading!

When he energized the circuit then the RCD tripped. Did a 2nd IR test and then dead short. - Don't understand this - its like the IR test caused the fault
 
Might have been a cable snagged after R1+R2 like you said 1shortcircuit

It may not even have been visible. I've had it on an MK socket before where there is just enough pressure between a conductor and the protective bar that runs across the back of the socket to cause this issue. Cable fine once repositioned.

I also had it on a light switch. Removed metal switch plate, replaced and the fuse popped (rewireable) It was one of those daft flat plate ones and on closer inspection I noticed that there was not enough room in the back box for the cables AND the switch unit. Replaced for a plastic one and advised client that deeper box was required.

Easily done I guess:thumbsup
 

Reply to Dead Short after IR testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
764
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top