when doing an inspection i came accross a radial circuit serving 4 points, the IR between L-N @500V was 0.00 Mohms, on continuity between L-N I got 25 ohms. when I then energised the circuit and clamped the live, no current being drawn. I have yet to take any fronts off as it was just an inspection and i didn't want to start faultfinding, i'm almost certain i got the whole of the circuit and everything was unplugged and they were just plain 2G sockets with no neons, but this one has baffled me. surely if the reading was that low, then there would be about 10A being drawn?
 
You have a light plugged in, could be a lamp, neon on a FSU, (check emersion heater), shaver point if on lighting circuit

keep looking and you will find something!

I did come across a FSU the other day hidden behind a false wall, home owner extended a ring with a FSU.
 
shaver point! i don't know for sure, but this seems likely as the radial is for a hallway, utility and bedroom right next to the bathroom. it's there is no loft, just really high ceilings so it can't be that. i'm back there this week sometime i'll investigate further
 
Next-door neighbours illicit grow room? (Oh No not that subject again)!

As the others have said you’ve overlooked a load somewhere. Let the hunt begin.

Are you going to tell us what you find?
 
mmm trying to think of a load that gives a 25ohm dc resistance but could be much higher impedance on ac. It could be a big heater load like an immersion or it could be a small electro-magnetic load like a shaver point or motor of some type. Dont know what the dc resistance on a fluorescent light but suppose its around that amount.

Good Luck and lets have a pic of the offending item

*hite just spotted no current drawn ? (or very small for your meter) Shaver point for me
 
Last edited:
My bets on an immersion heater hidden in a cupboard.
An immersion heater in a tank of hot water is favourite:- 1) When you tested the insulation the hot water in the tank was below the set temperature and the thermostat was therefore ON presenting a load. 2) When the final circuit was re-energised, the hot water quickly rose above the set temperature switching OFF the thermostat and disconnecting the load before you had clipped the clamp meter on to monitor the load current.
 
Last edited by a moderator:

Reply to dead short L-N but the fuse doesn't blow? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
764
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
984

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top