Evening all ,
Called out to short circuit on cooker circuit assumed that cupboard fitted above isolater switch screwed through cable , disconnected at switch then dead tested back to board
Continuity l- cpc .22
l-n .16
n-cpc .22
Ir test l-n 999
l- cpc 999
n-cpc 999
All passed yet still shorted out any ideas plan to replace whole cable.
 
I would have thought the IR test would have shown any screw through the cable. There is nothing shorting within the isolator when you screw it back is there. Why don't you redo the IR test with the isolator connected.
 
I would have thought the IR test would have shown any screw through the cable. There is nothing shorting within the isolator when you screw it back is there. Why don't you redo the IR test with the isolator connected.
I thought IR test should have picked it up most confused that it did not , left cable free to air just choc blocks not connected at all thinking isolater problem still tripped mcb . must be cable pierced a fraction ?
 
Why have you decided the fault lies with this cable, there is more to the circuit than the cable to the isolator. Test it all.
What voltage did you do the IR testing at?
240 and 500 volts
What voltage did you do the IR testing at?
Why have you decided the fault lies with this cable, there is more to the circuit than the cable to the isolator. Test it all.
IR test at 240 500 volts , New cupboard fitted above isolater switch led me to think cable damaged from isolater back to board .
 

Reply to Dead test fail? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
756
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
325

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top