Evening all ,
Called out to short circuit on cooker circuit assumed that cupboard fitted above isolater switch screwed through cable , disconnected at switch then dead tested back to board
Continuity l- cpc .22
l-n .16
n-cpc .22
Ir test l-n 999
l- cpc 999
n-cpc 999
All passed yet still shorted out any ideas plan to replace whole cable.
 
Evening all ,
Called out to short circuit on cooker circuit assumed that cupboard fitted above isolater switch screwed through cable , disconnected at switch then dead tested back to board
Continuity l- cpc .22
l-n .16
n-cpc .22
Ir test l-n 999
l- cpc 999
n-cpc 999
All passed yet still shorted out any ideas plan to replace whole cable.
Disconnect at the cooker itself and the board leave cpc connected to earth bar and test again at 500v
 
still think you may be correct in assuming a screw in cable. i once had a short on a socket RFC L -E caused by nicked L shorting to back box. MCB tripping but showed clear on 500V IR test.
 
What mft are you using and is it in calibration.? Ive never heard of a 240v IR test. You seem certain it is a damaged cable by the screw but test results youve put up would indicate the problem lies elswhere, but you are the one on site so you have the benefit of being there. What was zs at cooker isolator.?
 
What mft are you using and is it in calibration.? Ive never heard of a 240v IR test. You seem certain it is a damaged cable by the screw but test results youve put up would indicate the problem lies elswhere, but you are the one on site so you have the benefit of being there. What was zs at cooker isolator.?

Hard to measure this with MCB banging out
 
Your IR test should show up any issues. However If you can see the Heads of the screws on the new cupboard you could disconnect the cable connect all 3 conductors together and using a long lead check for continuity between screw heads and connected end of cable.
 
To add my morsel;
what history of this fault, did the customer give you?
what range of insulation resistance are you using, 999?
as others have suggested, mcb might be faulty, could you try another mcb temporarily in the CU?

PS, the continuity results, do their correlate with the suspected length of cable?
 
Try IR testing between L and and earth of another circuit, had a fault on lighting circuit where testing cable alone showed no fault but when testing the live to an earth on the rfc it showed a short, turned out new boiler had been fitted and screw had just nicked the live and was shorting through boiler case.
 

Reply to Dead test fail? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
756
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
327

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top