mrloy99
-
- Joined
- Dec 21, 2008
- Messages
- 473
- Reaction score
- 18
I wonder have any of you motor experts any thoughts on this.I was testing a plantroom today with many 3phase isolators fitted for pumps and panels etc. The isolators used were 4 pole rotary type(20 amp mostly).The installing electrician who wasn't present had connected up only the three phases to the switch and the neutral to the solid link inside the switch.I am wondering why not just connect the neutral thru the switch also.. The only info I can find in the BGB says that it is permitted to connect this way,I had assumed as a cost factor,ie a three pole switch is probably cheaper than a four pole switch...But what advantage is there in having a permanent neutral and having the bother of crimping the blue wire too.I realize that in most of these pumps a neutral wont be required anyway,but it cost me hours today at the panel which I thought was switched off at the isolator,the neutral wasn't and was giving me a very poor reading to earth on ir testing(0.10m ohms neutral to earth) I'm just hoping I havn't damaged something inside the control panel.