I Think you mean how do you apply derating factors to cables?

You need to be aware of:

The design current
The tabulated current carrying capacity of the cable
The ambient temperature
The grouping factor
Any thermal insulation factor
Voltage drop
 
Last edited:
I think ive confussed my self as I thought that how this question was worded was saying that if part of the run was to go through an area which has a 40 degrees C amient temperature from a 25 degreees C ambient temperture run I would need to decrease the current carrying capabilities of the cable. But what I think it is saying is that the current carrying capabilities of the cable will be reduced when it enters this 40 degrees area and therefore I will need to up my cable size.......


here was the question


a 70 degrees thermoplastic insulated and sheathed cable to bs6004 is installed in an ambient temperature of 25 degreees for part of the run and then enters an area at 40 degrees. the effect on the cable will be to

a) require clips at greater intervals
b) reduce the voltage drop
c)increase the bending radius
d)decrease its current carrying capacity
 
well if you think logically, the part of the cable installed in the higher ambient temperature will require less current to increase it's temperature to it's rated maximum operating temperature, so effectively, you will be reducing its CCC.
 
so does that mean you would need to concider uping the overall size of the cable. I mean if the current carrying capabilitie of the cable are to decrease will it effect the operation of the load or am I way of the mark
 
you need to apply the relevant rating factor according to the installation method. if the load current is less than the derated value of CCC , then the cable is OK for that situation.

e.g. 2.5mm is rated at 27A clipped direct. if it's installed ref. method 101, say, then the CCC is reduced to around 18A ( guesstimate as i not got osg handy) . so if you load is <18A you're OK. if it.s 23A, then you would need to increase the cable size.
 

Reply to decreaseing current carrying capacity in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

  • Question
You don't normally see It in the equation. What you would normally do is apply correction factors then select a cable/conductor for Iz from It...
Replies
7
Views
559
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
661

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top