SimpleSimon
Who would like to give their definition of a 'clean earth' when being used with IT/data equipment? My understanding would be an earth that goes back to the Original MET of the buildings incomer, by-passing any earthing terminals found in sub-boards?
Here's my scenario-
Condition Report on a large shop floor last night. One sub board identifies Tills marked as 'Clean Tills' and one marked 'Dirty Tills'. So an educated guess (and the other Spark with me who has been on site previous telling me it means clean earth) has bought me here. But the earth is exactly like the ones for the 'dirty tills', terminated in the same Sub-board earth terminal. I than begin thinking, maybe it is a high integrity earth for the socket outlets, but they are run in radials without the earth run in a ring?? They are also not terminated in seperate CPC terminals behinf the socket outlets. And no mention of any high integrity earth on the board either.
So Ive coded C3 further investigation, my plan is to use an earth leakage clamp, take a reading of the clean tills. If over 10mA than suggest circuit have its earth run as a ring.
If under 10mA, than I'll just readjust the wording of the circuit decription.:biggrin5:
Here's my scenario-
Condition Report on a large shop floor last night. One sub board identifies Tills marked as 'Clean Tills' and one marked 'Dirty Tills'. So an educated guess (and the other Spark with me who has been on site previous telling me it means clean earth) has bought me here. But the earth is exactly like the ones for the 'dirty tills', terminated in the same Sub-board earth terminal. I than begin thinking, maybe it is a high integrity earth for the socket outlets, but they are run in radials without the earth run in a ring?? They are also not terminated in seperate CPC terminals behinf the socket outlets. And no mention of any high integrity earth on the board either.
So Ive coded C3 further investigation, my plan is to use an earth leakage clamp, take a reading of the clean tills. If over 10mA than suggest circuit have its earth run as a ring.
If under 10mA, than I'll just readjust the wording of the circuit decription.:biggrin5: