I thought I had better add to welchyboy's post.
The 1.8 factor is not applied to the connected load of the fluorescent luminaires, it is applied to the protection device. It is applied to the circuit protection device to ensure that the circuit breaker will not trip when the lights are switched on.
Also as another poster has indicated the connected load is not 30 x 2 x 58w. You need to account for control gear losses, which can be in the region of between 5% to 10% of the lamp rating. It's best to take the manufacturers details for an accurate total luminaire watts.