Could someone explain what is involved when you have numerous correction factors

I have - ambient temp = 0.79 Thermal insulation = 0.88 grouping = 0.52 and a design current of 14.8A

Thanks
 
It = 14.8/ ( 0.79 x 0.88 x 0.52) = 40.94 A so look up the correct size and type of cable that has a tabulated ccc > 41A
 

Reply to Derating Factors in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Question
No worries.
Replies
3
Views
765
Yeah when we start up the cone crusher the power factor can drop from .9 to .5. I’ve seen it drop down to .4 during start up. We have more than...
Replies
5
Views
702

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top