No Malcolm you are correct, I don't have to answer or read.
However, I would consider not responding to you as being rude.
You obviously addressed your first post on this thread to me : "Afraid to say that the regs have scuppered that now spin, as the point of reduction in CCC can not be applied for branch circuits or socket outlets as in reg 434.2.1. This was newly introduced in the amendment."
I'm not trying to tell you that Regulations have been altered that haven't and ones that have been altered haven't.
You told me that there had been an alteration
I'm trying to tell you that the alterations make no difference.
The fact that the Regulations now require that there is no branch circuits or socket-outlets between a point of reduction in CCC and the position of an earth fault protective device is not really relevant, as all it does is bring it into line with the requirements for positioning the overload protective device, which the OP has already stated will be complied with.
The device the OP intends using provides both earth fault and overload protection, but apart from that, earth fault protection is already provided by an RCD at the origin of the circuit. As such 434.2.1 is not applicable.
What difference does the change in 434.2.1 make in the OP's situation? None whatsoever.
There are instances where overload protection can be omitted alltogether, as long as certain criteria are met see 433.3.1.
The OP's situation appears to be one of those instances.