Hi Guys please feel free to pick the following to pieces just trying to put the theory into practise. I'm going to rewire my house as part of my assesment, 3 bed victorian terrace, below is a picture of the distribution with 6mm t&e (I think ) feeding the CU from a henly block, no main switch. TN-S earth neutral system.Fuse 100A ? (doesn't say)
[ElectriciansForums.net] Design


1, Consumer Unit
a, Detach tails from henley and put in place main isolater switch 100A REC2S

b, from isoator to henly block 25mm² tails

c, from henley to CU 25mm² tails into 63A main switch

d, renew main bonding and MET 16mm² MET to CU

e, 10mm² to incoming gas and water with appropriat labelling

f, split 10 way CU with 2 x 30mA RCD rest type B MCB
2, Beyond the C/U

a, final ring down 32A mcb RCD protected 2.5mm² 9 double sockets

b, final ring up 32A mcb rcd protected 2.5mm² 12 double sockets 1 FCU (combi boiler)

c, final ring kitchen and utility 32A mcb rcd protected 2.5mm² 6 double sockets 4 FCU (various int. appliances)

d, radial for oven and hob 40A mcb rcd protected 6mm²

e, lights down 6A mcb rcd protected 1.5mm² 6 40w spots 6 100w lamps

f, lights up 6A mcb rcd protected 1.5mm² 10 40w spots 4 100w lamps

g, lights kitchen back and exterior 500w security 8 40w spots 4 100w lamps

3, Garage

a, 2.5mm² SWA from 32A mcb in main CU to 30mA RCD in garage CU

b, small ring 2.5mm² 32A mcb

c, light 1.5mm² 6A mcb

Testing I'm fine with but will learn more when I physically do it rather than trying to soak up sequencies and regs from endless books.

Phewwww got there in the end this is my proposed design and actually have already answered a few of my questions writing this. Does this seem ok, overkill, or wrong please let me know :)

 

Reply to Design in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
711
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top