I hope this is in the right section.
I am hoping someone can refer to the correct section in 7671.
Incoming TNCS/PME
Brother in laws house 80's, set in CU with type 1 breakers no RCD protection at all.
( No funds for new board )
Detached garage T&E comes out of board to outside in to an adaptable box and continues into garage in SWA. 2 Way rewire-able fuses Looks like SWA is only 2 core but difficult to see
As per the old regs ( I think ) they have run no CPC from the dwelling instead earthing is provided by rod. IE a TT system
Additional protection is provided by a 30 mA oldd rccb, RCD tested trips on both 0/180 well within limits.
Measured Ze in garage is high at 68 Ohms but I believe this falls within the parameters for TT.
I want to submit this a board change for Part P assessment, I think and this is where I need the help guys that I should be looking at running a 16mm csa main earth back to the board or a met block in the outside meter box ( this would be easier as the main Earth from the PME disappears into the cavity ) as I am paying for the project I was planning on a 4 way board + MS with an RCBO for lights/sockets/pond/spare.
I do have all the readings ie Ze/Zs and pfc's for both buildings if this in anyway makes any difference to the answer given
As always thankful for your advice guys !
ATB Steve
I am hoping someone can refer to the correct section in 7671.
Incoming TNCS/PME
Brother in laws house 80's, set in CU with type 1 breakers no RCD protection at all.
( No funds for new board )
Detached garage T&E comes out of board to outside in to an adaptable box and continues into garage in SWA. 2 Way rewire-able fuses Looks like SWA is only 2 core but difficult to see
As per the old regs ( I think ) they have run no CPC from the dwelling instead earthing is provided by rod. IE a TT system
Additional protection is provided by a 30 mA oldd rccb, RCD tested trips on both 0/180 well within limits.
Measured Ze in garage is high at 68 Ohms but I believe this falls within the parameters for TT.
I want to submit this a board change for Part P assessment, I think and this is where I need the help guys that I should be looking at running a 16mm csa main earth back to the board or a met block in the outside meter box ( this would be easier as the main Earth from the PME disappears into the cavity ) as I am paying for the project I was planning on a 4 way board + MS with an RCBO for lights/sockets/pond/spare.
I do have all the readings ie Ze/Zs and pfc's for both buildings if this in anyway makes any difference to the answer given
As always thankful for your advice guys !
ATB Steve