If you have no other services in the garage and provided the earth in the sub main can handle the PEFC you could remove the earth rod and connect the earth from sub main into garage cu.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Detached garage and regs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I hope this is in the right section.
I am hoping someone can refer to the correct section in 7671.
Incoming TNCS/PME
Brother in laws house 80's, set in CU with type 1 breakers no RCD protection at all.
( No funds for new board )
this could be done using a budget board ie:cpcConsumer Units & Enclosures not brilliant boards but great where budget is tight ,also could form part of your part P assesment
Detached garage T&E comes out of board to outside in to an adaptable box and continues into garage in SWA. 2 Way rewire-able fuses Looks like SWA is only 2 core but difficult to see
As per the old regs ( I think ) they have run no CPC from the dwelling instead earthing is provided by rod. IE a TT system
Additional protection is provided by a 30 mA oldd rccb, RCD tested trips on both 0/180 well within limits.
Measured Ze in garage is high at 68 Ohms but I believe this falls within the parameters for TT.
I want to submit this a board change for Part P assessment, I think and this is where I need the help guys that I should be looking at running a 16mm csa main earth back to the board or a met block in the outside meter box ( this would be easier as the main Earth from the PME disappears into the cavity ) as I am paying for the project I was planning on a 4 way board + MS with an RCBO for lights/sockets/pond/spare.
I do have all the readings ie Ze/Zs and pfc's for both buildings if this in anyway makes any difference to the answer given
As always thankful for your advice guys !
ATB Steve