If you have no other services in the garage and provided the earth in the sub main can handle the PEFC you could remove the earth rod and connect the earth from sub main into garage cu.
 
If Ze at the garage CU is <100Ω why bother ripping out the electrode and running in another earth?
The garage is effectively it's own installation with it's own earthing system.
Surely better than transporting the earth from TNCS?
 
I hope this is in the right section.

I am hoping someone can refer to the correct section in 7671.

Incoming TNCS/PME

Brother in laws house 80's, set in CU with type 1 breakers no RCD protection at all.
( No funds for new board )

this could be done using a budget board ie:cpcConsumer Units & Enclosures not brilliant boards but great where budget is tight ,also could form part of your part P assesment
Detached garage T&E comes out of board to outside in to an adaptable box and continues into garage in SWA. 2 Way rewire-able fuses Looks like SWA is only 2 core but difficult to see

As per the old regs ( I think ) they have run no CPC from the dwelling instead earthing is provided by rod. IE a TT system

Additional protection is provided by a 30 mA oldd rccb, RCD tested trips on both 0/180 well within limits.

Measured Ze in garage is high at 68 Ohms but I believe this falls within the parameters for TT.

I want to submit this a board change for Part P assessment, I think and this is where I need the help guys that I should be looking at running a 16mm csa main earth back to the board or a met block in the outside meter box ( this would be easier as the main Earth from the PME disappears into the cavity ) as I am paying for the project I was planning on a 4 way board + MS with an RCBO for lights/sockets/pond/spare.

I do have all the readings ie Ze/Zs and pfc's for both buildings if this in anyway makes any difference to the answer given

As always thankful for your advice guys !

ATB Steve

hope this helps
 
I am grateful for time and trouble you have taken to read this thread fella's .

I am not one to follow regs blindly I want to understand the principle behind a regulation and then adopt it based on my understanding of it, perhaps I am too ---- and should just follow the carrot, I now understand the principle of other services entering and the need for them to be EB back to to MET.

If this was a cottage in the middle of nowhere I wouldn't even be having this discussion I would assess it as TT, deal with it as TT and move on, the reason I am being so paranoid about it is because the garage is less than 3 foot from the house, has outside supplies to garden pond, and I can't seem to reconcile in my mind the the poor Ze compared to the house, but I except this is within the regs and and see if I can get the main CU changed instead, and just earth the CPC on the supply side only.I think I would prefer to have an mcb at CU and a D/P RCD in garage as opposed to an RCBO. Thanks again.

ATB Steve
 

Reply to Detached garage and regs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
625
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
955

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
322
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top