Hi telectrix, if i was to TT the garage, there would still be a path back into the house via the bonded central heating pipework.
 
The detached garage is no more than 5 metre`s from the house.


No problem then!! Should of asked you to advise in the first place, ...that or run the existing cable in a duct as Tel suggested!! lol!! Try conducting a sheath test on that cable your mate has installed, ...what's the betting it fails?? lol!!
 
Hi telectrix, if i was to TT the garage, there would still be a path back into the house via the bonded central heating pipework.

Because of this, it is unlikely that you will be able to isolate the garage from the house (unless plastic is used in the pipework). 10mm bonding cable is the way to go imo.
To put your mind at rest, why not speak to your scheme provider :)
 
Yes, that could be interesting, to say the least.
Am i right in saying that the copper equivalent for the armoured is 7.39?


Let's put it in these terms, ...there is no way the existing 6mm SWA cables armour is going to provide your bonding requirements, so it's either changing existing cable for a 3 core 10mm SWA, (whose armour Still wouldn't comply for bonding purposes) or run in a separate 10mm bonding conductor!! lol!!

Steel requires about approx 8 times the CSA of a complying copper conductor, for it to be equivalent/suitable for bonding purposes!!
 

Reply to Detached garage in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
117
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
341
Are you sure the existing outside socket is on the ring, and not already a spur? I tend to place a switch fuse on the ring inside so that the...
Replies
1
Views
201

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top