We are having trouble getting any G59/3 applications passed around here now I'm not talking Gavin or Jason stylee but 6-12KWp
Is there a reasonably priced way to prevent export and comply with the above?
National Grid has informed us that we cannot connect any further generation to our site at Burwell Main Grid, which is the point at which we connect with National Grid, without submitting a statement of works. This statement of works attracts a non-refundable fee of ÂŁ7500 which would need to be paid by the customer in advance. The current guidance from National Grid is that any additional generation connections would require a new Super Grid Transformer. This would also mean substantial reinforcement work on our network.
We do allow the use of devices to restrict export, but in those cases we will want to witness test the installation to ensure the device is effective for which there is a fee of ÂŁ900 + VAT. If you wish to install a device to restrict export the export would have to be set to zero for the entire system. I realise this may seem illogical but there are reasons for us adopting this position.
Is there a reasonably priced way to prevent export and comply with the above?