L

lionelmcc

I just got some new certs. Asks for disconnection times in circuit info
can someone tell me where 5s disconnection applies under the 17th edition
as it does not seem to be just hard wiring or sockets anymore (Big red is making me Dizzy)
 
In a TN 230V system, maximum disconnection time for final circuits up to 32A is 0.4 seconds. Final circuits exceeding 32A are permitted up to 5 seconds. BS7671 411.3.2
 
In a TN 230V system, maximum disconnection time for final circuits up to 32A is 0.4 seconds. Final circuits exceeding 32A are permitted up to 5 seconds. BS7671 411.3.2

Dont forget distribution circuits e.g. main CU to garage CU, this sub main is also permitted 5sec
 
I think the proective device must be greater than 32 amp to allow 5 secs rather than 0.4. Most cooker circuits are 40 or 45 amp so 5 secs is allowed.

Page 282 of the regs indicates that if the cable was 4mm then depending on the ref. method the CB would be unlikely to be greater than 32 amps therefore min. cable size must be 6 or 10mm.
 
I thought if a cooker switch incorporates a socket outlet then the disconnection time is ALWAYS 0.4 sec regardless of the size of the MCB but I can't find it in the regs.
 
I thought if a cooker switch incorporates a socket outlet then the disconnection time is ALWAYS 0.4 sec regardless of the size of the MCB but I can't find it in the regs.

Your bang on mate. But he said without a socket outlet it can be 5 seconds disconnection time. But if its only 32A then its still 0.4seconds.

Cheers
 
Disconnection Times


230v final circuits in a TN system not rated greater than 32A must disconnect within 0.4 seconds under fault conditions. 411.3.2.2
230v final circuits in a TT system not rated greater than 32A must disconnect within 0.2 seconds under fault conditions. If disconnection is made by a fuse or mcb and all extraneous conductive parts are connected to the main equipotential bonding then a disconnection time of 0.4 seconds is permitted. 411.3.2.2
Under fault conditions in a TN system, circuits over 32A including distribution circuits must disconnect within 5 seconds. 411.3.2.3 Under fault conditions in a TT system, circuits over 32A including distribution circuits must disconnect within 1 second. 411.3.2.
All this can be found in the sticky Brightspark posted.
BS7671 : Reference
 
Last edited by a moderator:

Reply to Diconnection times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D
  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top