And don't assume there is always just one fault,there may be more or an accumulation.

Boydy
 
Ok, I swung by on way home and sure enough the ze at the origin is 3.5 ohms so all four flats are affected. Have emailed my office saying as a matter of urgency we need to contact the supplier.
I always thought that a rcd looked for an imbalance between neutral and earth,and a mcb took care of overcurrent and short circuit and earth fault, hence being stumped after removing all neutrals from the board and even removing the outgoing neutral from the rcd and the rcd still tripping
Hi Pondy,an RCD does monitor and operate due to an imbalance,but between line and neutral,this may be shootin' up THE earth,or AN earth,but it determines "some",maybe 30 ma's worth is awol,and operates accordingly. The advice concerning the order of tests is sound,and although on occasion skipping some can still bring a quick result,in general it negates back-tracking. Happy hunting.
 

Reply to Didn't think was possible in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
349
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
499

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top