And don't assume there is always just one fault,there may be more or an accumulation.

Boydy
 
Ok, I swung by on way home and sure enough the ze at the origin is 3.5 ohms so all four flats are affected. Have emailed my office saying as a matter of urgency we need to contact the supplier.
I always thought that a rcd looked for an imbalance between neutral and earth,and a mcb took care of overcurrent and short circuit and earth fault, hence being stumped after removing all neutrals from the board and even removing the outgoing neutral from the rcd and the rcd still tripping
Hi Pondy,an RCD does monitor and operate due to an imbalance,but between line and neutral,this may be shootin' up THE earth,or AN earth,but it determines "some",maybe 30 ma's worth is awol,and operates accordingly. The advice concerning the order of tests is sound,and although on occasion skipping some can still bring a quick result,in general it negates back-tracking. Happy hunting.
 

Reply to Didn't think was possible in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
541
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
918

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
421

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top