Don't know about the Diehl, but i installed a SB4000TL recently and the instructions said if using an RCD not to be lower than 100mA. I put it on a standard MCB as the circuit supplying the inverter didn't need an RCD under BS7671.
You sure you need an RCD at all?
hi there ive fitted about 30 diehl heavy bloody units those 3800s i have never had any problem with these inverters apart form back ache!! never had rcd trip on us either do a ramp test on rcbo check its tripping times
SolarCity is right about the spec's of the 3800S (MPP range of 315-630VDC), assuming they are the mono HJ panels, they have a 60V Voc so 16 panels in one string could be hitting between 800VDC and 1000VDC on a cold/crisp day (in theory). As advised, try splitting into 2 strings of 8 panels and re-connecting to the inverter but it is possible that damage has already been done to the inverter although I would have expected an overvoltage error to have been flagged up.