Neither the SMA or the Power-one will cope with a single string the MPP voltages are too high in cold wether conditions. Fire it up as a single string and you will damage the inverter.
As the Diehl 3800TLD only has a single MPP tracker, it needs to be configured as two identical strings ( 2 x 8) to avoid damage to the inverter, although even then the MPP Voltage range is outside the tracking range of the inverter. This is in simple terms a very bad design and a mismatch with the inverter. Whowever designed it / specified it should have checked the parameters first.
As 2 x 8 , it won't blow up, however it will perform well below its capabilities. You should swap the inverter for a Power-one OUTD 3,6 or SMA 3600TL
See attached from PV*SOL output for the Diehl 3800TLD when configured as a single string.
![Fullscreen capture 28122012 123315.bmp.jpg Fullscreen capture 28122012 123315.bmp.jpg](https://electricians.s3.eu-west-1.amazonaws.com/data/attachments/9/9909-5a6df2ec96ae1613384782309ac63aa4.jpg?hash=Wm3y7JauFh)
As the Diehl 3800TLD only has a single MPP tracker, it needs to be configured as two identical strings ( 2 x 8) to avoid damage to the inverter, although even then the MPP Voltage range is outside the tracking range of the inverter. This is in simple terms a very bad design and a mismatch with the inverter. Whowever designed it / specified it should have checked the parameters first.
As 2 x 8 , it won't blow up, however it will perform well below its capabilities. You should swap the inverter for a Power-one OUTD 3,6 or SMA 3600TL
See attached from PV*SOL output for the Diehl 3800TLD when configured as a single string.