Hello,

I’m testing some electric meters.
As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and put the ct around the line of the hair dryer to check measurements are the same as a calibrated meter.
The Ct’s from each phase read the same Amps however the kw reading is twice as high for the L2 Ct which is the circuit the socket is plugged into.
This also occurred when the sockets where L3 circuits in a different location then the L3 ct had twice the kw but the same amps as the other phases.
This was the same every time.

Would anyone know why this occurs ?
Many thanks
 
I think a diagram could help, also i assume your KW readings are from the meter you are testing. Again assume your hairdryer is single phase and the meters are three phase. How the meters are connected ? Type of meter?
End of the day to get accurate KW you need an accurate current and an accurate voltage.
 
I think a diagram could help, also i assume your KW readings are from the meter you are testing. Again assume your hairdryer is single phase and the meters are three phase. How the meters are connected ? Type of meter?
End of the day to get accurate KW you need an accurate current and an accurate voltage.
hi,
Yes your right single phase dryer, Carlo gavazzi 271 meters and yes the reading is from the meter.
 
Have fitted those before. Not wanting to state the obvious but it is vital that the voltage inputs to the meter, L1, L2, L3 match exactly with the L1, 2, 3 current transformers. i.e. the line that you designate as L1 for voltage has to be the same line you designate for L1 for the CT
Please see connection diagrams in https://www.gavazzi.no/wp-content/uploads/EM271DS.pdf
Dont forget the neutral connection to the meter , also
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Different kw readings
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Estiban,
Last reply from
plugsandsparks,
Replies
3
Views
949

Advert

Back
Top