I have come across a fault that I am struggling to find. I cant remember being stumped like this before as I like fault finding and have always found the fault before.

6A MCB is tripping on lights. It sometimes trips the moment it is switched on and sometimes takes up to 30 mins. There is no RCD.

IR readings are poor (o.3Mohms L/N - E) but do not show a short circuit to earth. I have removed all lamps but IR readings for L-N still suggests something is on the circuit which I cannot find (0.05Mohms).

I have tried it on another 6A MCB, it trips, so not a faulty MCB.

It will not be an over current as there is little on the circuit (2 bathroom lights, 1 x kitchen, utility, garage, perhaps 2A absolute max).

My plan is now to break the circuit in half and leave. Customer can tell me if it trips or not. I can carry on like that but it means many trips and they are not close.

I could also try it on the RCD side to see if it trips the RCD (meaning a L-E fault, but would this knowledge help?)

Any suggestions?
 
Yes I could, but would this not just show the 1 or 2 A running through it at that time? It may change rapidly when it's about to trip but I don't think I can get away with standing there for 30 mins :)
Anyway, I am now leaving to find it!
Glad you found it! If you put 10a through a 6a mcb it will take a while to trip, and it wasn't clear if the trip was from overload or fault. The idea was also to work out if it's going down l-n or l-e or l-cpc.
Glad you're sorted though!
 
it wasn't clear if the trip was from overload or fault

I think it was though. HHD reckoned on a couple of amps load on the circuit, and anything else consuming 1500VA or so would have made its presence felt. Had the MCB been tripping through being on the threshold of its current rating, a) it would have been warm which HHD would hopefully have noticed and b) the tripping would be more cyclic than random. It's useful to consider the power dissipated at a suspected fault and what damage it would cause. 1500W dissipated at a point fault would soon set it on fire or melt it so extensively that it could not have remained as it was to cause another trip. So it had to be an intermittent short-circuit, that did not blow itself clear completely on account of the low rating of the MCB and moderately high resistance of the small cable. Had the same damage occurred on a cooker circuit near the board, it would be more likely to blow itself apart at the first bang.

It had classic symptoms of a damaged cable - very low IR L-E and N-E with occasional tripping of the MCB. There was no certainty that each of the abnormal symptoms was related to a single fault but the principle of Occam's razor would suggest so. Easy to analyse with hindsight, of course.
 
Agree totally and thanks for the analysis, i only wanted to add it to the mix as a consideration as no point in saying "i thought that originally" after the fact!
Just a couple of points that may be interesting..
If an MCB trips in overload it can trip again quickly due to it already being very warm
Also the fault i suggested was a faulty psu for lights or similar. A transformer with shorted windings can warm up a lot without causing a fire
 

Reply to Difficult fault to find? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
870
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top