I've recently put a new circuit in a house and when filling out my EIC, I needed to access the service head (attached).

I'm relatively new to this and I'm struggling here.

In order to access ANY part of this, you have to pull the main fuse and I had to cut a few metal tallys off. As you can see on the left is where the main fuse sits, to the right there is a cover for the MET and underneath is a cover for the incoming cables. The black box between the meter and thefuse housing is not removable - I can't see where the main earth is. The earth cable you can see is bonding from the gas pipe.

Also, immediately I thought it was a TNS system but it gets quite strange. The what looks like SWA is not SWA, it looks and feels like copper!! IT DEFINITELY isn't steel. Additionally, I can't find a neutral anywhere, I can't see if it is in with the red incoming wire but I'd be pretty surprised if it was.

Could the copper SWA (I know) actually be the PME neutral and we are actually looking at a TNCS system here?

Either way, I have never seen anything like this cable before.

Thanks in advance, I genuinely don't know if I'm just being stupid or inexperienced here but I'm kinda stuck with a way ahead.

View attachment 35655

View attachment 35656

View attachment 35657
 
Hello all,

I've recently put a new circuit in a house and when filling out my EIC, I needed to access the service head (attached).

I'm relatively new to this and I'm struggling here.

In order to access ANY part of this, you have to pull the main fuse and I had to cut a few metal tallys off. As you can see on the left is where the main fuse sits, to the right there is a cover for the MET and underneath is a cover for the incoming cables. The black box between the meter and thefuse housing is not removable - I can't see where the main earth is. The earth cable you can see is bonding from the gas pipe.

Also, immediately I thought it was a TNS system but it gets quite strange. The what looks like SWA is not SWA, it looks and feels like copper!! IT DEFINITELY isn't steel. Additionally, I can't find a neutral anywhere, I can't see if it is in with the red incoming wire but I'd be pretty surprised if it was.

Could the copper SWA (I know) actually be the PME neutral and we are actually looking at a TNCS system here?

Either way, I have never seen anything like this cable before.

Thanks in advance, I genuinely don't know if I'm just being stupid or inexperienced here but I'm kinda stuck with a way ahead.

View attachment 35655

View attachment 35656

View attachment 35657
Put it all back together, clean your finger print and any DNA from the area, claim you had amnesia if anyone says anything, you shouldn't be frolicking about inside the head it's not yours to play with.
 
Ok to confuse things more the Ze test is If that is a Gas bond, how did you measure Ze without verifying the earthing conductor 0.11 ohms - it is not TT.

That earth you can see is 100% definitely the gas pipe bond.

If that is a Gas bond, how did you measure Ze without verifying the earthing conductor
 
OP, as already advised by members, think you just need to go back to basics, and verify earthing conductor and main bonding conductors, just in case you've made a mistake. We are all human.
 
I understand that I may have been hasty to take apart the service head but I have a job to do and I don't want to be wasting time. I'm not going to lose any sleep about cutting some tallies off. I'll phone up the suppliers, If they're going to get upset about it then I'll take it up with them.

Now to sound like a complete -------: while I'm new to the domestic game (and service heads!), I am an electrical engineer trained to degree level through an apprenticeship with 15 years experience in industrial electrics.

Then you should already be aware of concentric cable, test methods for establishing earthing arrangements, investigation methods for establishing methods of earthing, and remedial action to be carried out to rectify earthing problems.

I'm not belittling your qualification or experience, but degree or no degree, there still exists the probability of not having sufficient training for the task you are doing.
 
Think that's the main earth to the cu, any bonding conductors will/should be on the earth bar in the cu imo

I expect you joined the thread late Pete,I refer you to the post I made previously:)

quote
That 10mm or 16mm green /yellow is probably your earthing conductor from the cut out to your consumer unit
You can verify with a continuity test
At the consumer unit you may then find some bonding cables for services
 
Yep, I'm going to start again, this is turning into a mess.
Thanks for all the advice everyone.

Take a deep breath, and go through each step in a logical fashion.

Ps when you've done, I would certainly ask the DNO to have a look at their cable termination, they might fit a proper shroud or they might say it's fine. Least you can note you've done so on your EIC.
 
Then you should already be aware of concentric cable, test methods for establishing earthing arrangements, investigation methods for establishing methods of earthing, and remedial action to be carried out to rectify earthing problems.

I'm not belittling your qualification or experience, but degree or no degree, there still exists the probability of not having sufficient training for the task you are doing.

Absolutely, and I won't do it again. My point is that I understood what I was doing was dangerous - potentially fatal if done incorrectly. I wanted to visually check which earthing arrangement it was before carrying out a test and I was a bit hasty in dismantling the head whereas I should've done the tests. Lesson Learnt.
 

Reply to Difficult Service head in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

W
Definitely agree that you should leave well alone and contact UK Power Networks to sort it out. It is their problem and why should you pay an...
Replies
2
Views
421
Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
875

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top