Can anyone recommend a dimmer switch compatible with a light fitting which has a transformer and led G4 lamps
The light fitting is from next
Cheers
 
If the fitting came with the G4 LEDs then any low load dimmer should be OK to dim the driver, trailing edge dimmers tend to work better. Just make sure the minimum load is less than the load of the fitting.
 
I would say the chances of this working are somewhere between slim and none.

The fact it has G4 lamps and not an integrated LED suggests that it was designed for halogen capsule lamps not LED lamps, and so the transformer will be exactly that and not an LED driver.
 

Reply to Dimmer switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

Thank you. I guess i'll have to return this dimmer and find one without the Neutral. Thanks a lot for the help!
Replies
4
Views
401
  • Question
try a varilight pro dimmer for led's
Replies
3
Views
464

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top