Hi All,
Many thanks for all of your help so far. I thought I would post an update considering the installer returned on Tuesday.
p.s. I appreciate that some of the points in my update below may already mention things that you have all kindly advised about already, so I apologise in advance for repetition. I am starting to understand the basics, however am struggling with the exam question of “is it safe or not”?
Since the problem occurred, I have been in frequent email contact with the installer. The installer has also reached out to Dimplex, who have said it would be fine to install the off-peak element of the heater onto a ring main with the usual 32A breaker using a 20A double pole isolator before a 16A timer, assuming that loading, installation, grouping, Volt drop etc was in accordance with BS7671.
The installer therefore came round on Tuesday, and plugged this device into the plug socket which the heater was previously plugged into (before the plug melted). He took a reading of the impedance and explained that the low value means that installing the heater onto the ring main would be fine. Does this satisfy the tests that Dimplex mentioned?
He then proceeded to change the plug socket to a 20A DP switch, and connected it to a 16A timer which was installed beside it. This timer was then connected to the off-peak element.
We left the timer on an “always on” state temporarily to test that everything was working as expected, however after a few hours I noticed that the heater was blowing out cold air. All of the lights were on (on the 20A DP switch, and the timer), indicating that both new outlets were working, therefore I assumed that there was a lose/wrong connection between the timer and the heater. I switched the 20A switch off as I wasn’t going to be at home for a few days.
As you can imagine I was rather frustrated, thus I wrote a rather furious email back to the installer and demanded that these issues are rectified immediately. I also asked for written confirmation that the way in which the heater had been installed was safe and abiding to regulations. I therefore wanted them to accept liability if anything went wrong.
The installer replied and said that they would come and fit a dedicated wire from the fuse box to the room instead, all at their cost. They also said that they would hide the wire in trunking.
Fast forward to this weekend, when I turned the switch and timer back on and also factory reset the heater (I thought that if it was a charge problem, considering that the Quantum detects when it needs to charge and remembers when the electricity to the off-peak element is available and not, the factory reset would do the trick). I was surprised that the heater now worked as expected.
So now I am a bit unsure as to what to do. They have drilled a hole in the plasterboard to install the timer next to the 20A DP switch, so I don’t want a hole left there. At the same time, if there is any risk of danger in using the setup I currently have, I would rather them fit the dedicated wire and live with the annoyance of having a surface mounted wire extending from one end of the flat to the other, on my currently neat, clean and newly painted walls.
Advice would be much appreciated - they are scheduled to return to my flat next Saturday (12th March).
Many thanks in advance!
P.