Hi guys ths is my first time on here and relatively new to electrics. I was asked to find the times of disconnection needed for 5x and 1x. I was wondeering if anyone could give me a push in the right direction by pointing out where i could find such useful info inthe BS 7671 or onsite guide. THank you. Volers
As per the On-site Guide
- A disconnecting time of not more than 0.4 sec is required for final circuits with a rating not exceeding 32A.
- A disconnecting time of not more than 5.0 sec is required for final circuits exceeding 32A, and distribution circuits.
You have to enter the maximum value of x1 & x5 on your report sheet.
Hope this helps!
i am looking through bs7671 in the inspection and testing chapter, however I am unable to find the relevant info on disconnection times at different rated currents. Also it keeps referring in the book back to chap. 41. sorry to be a pain and asking such simpleton questions but i want to make it my single mission to get a better understanding of inspection and testing this week!!!
Hope this helps!
According to the table yellow van man has pointed out... the max trip time for 30 mA at 1x is 300ms.
Hi
When you test a 30 mA RCD you should start at : positiv side - O * (degree)
- 1/2 x I ^n (^ is delta) - (15 mA ) no trip within 2000mS
- 1 x I^n (30 mS) --trip within 200 mS
- 5 x I^n (150 mS) -- trip within 40 mS
repeat hte same at negativ side -180 *
you rec. the highest value ( longest time)
seems to be some confusion over trip times of MCBs and RCDs. RCD times are 300msec.@ x1. 40msec.@ x5. ( TT systems it's 200msec.@ x1. )
Reply to Disconnection times for 30mA RCD at 5 times current. in the Australia area at ElectriciansForums.net
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...