Hi guys ths is my first time on here and relatively new to electrics. I was asked to find the times of disconnection needed for 5x and 1x. I was wondeering if anyone could give me a push in the right direction by pointing out where i could find such useful info inthe BS 7671 or onsite guide. THank you. Volers
 
As per the On-site Guide

- A disconnecting time of not more than 0.4 sec is required for final circuits with a rating not exceeding 32A.
- A disconnecting time of not more than 5.0 sec is required for final circuits exceeding 32A, and distribution circuits.

You have to enter the maximum value of x1 & x5 on your report sheet.

Hope this helps!
 
i am looking through bs7671 in the inspection and testing chapter, however I am unable to find the relevant info on disconnection times at different rated currents. Also it keeps referring in the book back to chap. 41. sorry to be a pain and asking such simpleton questions but i want to make it my single mission to get a better understanding of inspection and testing this week!!!
 
thanks Goody ii didnt read your post before replying... thats great help. i think my main problem is trying to locate where to extract info from in the holy 7671 book.
 
As per the On-site Guide

- A disconnecting time of not more than 0.4 sec is required for final circuits with a rating not exceeding 32A.
- A disconnecting time of not more than 5.0 sec is required for final circuits exceeding 32A, and distribution circuits.

You have to enter the maximum value of x1 & x5 on your report sheet.

Hope this helps!




According to the table yellow van man has pointed out... the max trip time for 30 mA at 1x is 300ms.
 
i am looking through bs7671 in the inspection and testing chapter, however I am unable to find the relevant info on disconnection times at different rated currents. Also it keeps referring in the book back to chap. 41. sorry to be a pain and asking such simpleton questions but i want to make it my single mission to get a better understanding of inspection and testing this week!!!

Hi
When you test a 30 mA RCD you should start at : positiv side - O * (degree)
- 1/2 x I ^n (^ is delta) - (15 mA ) no trip within 2000mS
- 1 x I^n (30 mS) --trip within 200 mS
- 5 x I^n (150 mS) -- trip within 40 mS
repeat hte same at negativ side -180 *
you rec. the highest value ( longest time)
 
seems to be some confusion over trip times of MCBs and RCDs. RCD times are 300msec.@ x1. 40msec.@ x5. ( TT systems it's 200msec.@ x1. )
 
All disconnection times are listing in the On-Site Guide page 92. If you are taking your 2330 302/303 make sure you label your On-Site with post-its so you can access the information quicker.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Disconnection times for 30mA RCD at 5 times current.
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
volers,
Last reply from
topquark,
Replies
22
Views
82,090

Advert

Back
Top