Yes, as I said above but the disconnection time on the schedule of test results would still be recorded as 5 seconds whether the installation was under control of instructed/skilled persons or not.
I have a mail from IET technical help confirming this, I'll see if I can dig it out!

Didn't realize you was discussing what to put on the test paper, but I would still stick 0.4 in because there's a socket on the circuit, but that's just me I suppose.
 
Be careful how you interpret BS7671, it is not for example a requirement for circuits over 32A or a distrbution circuit to disconnect in 5 seconds 411.3.2.3, it is a permitted increase fundementally to allow discrimination to be achieved
 

Reply to Disconnection Times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
570
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
999
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
952
thats not what was stated though... they say the ocpd exceeds the ccc of the circuit... which to me means the cable. Loads can be disconnected/...
Replies
4
Views
536

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top