Sorry IQ i meant to say just the socket outlets in the home or if fed from a garage say
Yes but they would likely be on a 'A1 Ring Final Circuit with 32A protective device so would have a TN system disconnection time of 0.4 seconds.
Sorry IQ i meant to say just the socket outlets in the home or if fed from a garage say
Hi IQ,
Am in right in thinking then ,that for a L-E fault in the above scenario with the lawn mower for instance , the 0.4 s disc time is there to prevent elec shock and not cables being damaged causing fire etc. If this is the case then why in the bs7671 on page 46 ,note 1 at bottom of page says ,disconnection is not req for protection against elec shock but may be required
for other reasons such as thermal effects prevention?.
This is whats confusing me i think
kind Regards
LOCKET