disconnection times | Page 2 | on ElectriciansForums

Discuss disconnection times in the Talk Electrician area at ElectriciansForums.net

Sorry IQ i meant to say just the socket outlets in the home or if fed from a garage say

Yes but they would likely be on a 'A1 Ring Final Circuit with 32A protective device so would have a TN system disconnection time of 0.4 seconds.
 
Hi IQ,

Am in right in thinking then ,that for a L-E fault in the above scenario with the lawn mower for instance , the 0.4 s disc time is there to prevent elec shock and not cables being damaged causing fire etc. If this is the case then why in the bs7671 on page 46 ,note 1 at bottom of page says ,disconnection is not req for protection against elec shock but may be required
for other reasons such as thermal effects prevention?.

This is whats confusing me i think

kind Regards

LOCKET
 
Basic protection is the usual form of 'basic' shock protection ie. insulation of live parts etc.

Protection under fault conditions ensures that accessible conductive parts ie. metallic enclosures, pipes etc. must not be hazardous under single fault conditions.


ADS is used to limit the magnitude and duration of fault voltage between exposed, conductive and extraneous-conductive parts.


Where shock risk is increased (special locations etc.) then additional protection is required ie. RCD protection or supplementary bonding.
This also guards against failure of any of the basic/fault protection measures.
 
Last edited:
The 0.4 sec is part of ADS and is based on Biegelmeier and Lee's testing of human thresholds at 230 v.

Not sure about the 5 sec, but the bigger the circuit the larger the fault current required to disconnect, on large installations it will be difficult to generate enough current to disconnect within 0.4, so allowing upto 5 secs give some leeway.
 
Hi IQ,

Am in right in thinking then ,that for a L-E fault in the above scenario with the lawn mower for instance , the 0.4 s disc time is there to prevent elec shock and not cables being damaged causing fire etc. If this is the case then why in the bs7671 on page 46 ,note 1 at bottom of page says ,disconnection is not req for protection against elec shock but may be required
for other reasons such as thermal effects prevention?.

This is whats confusing me i think

kind Regards

LOCKET

Cables need to be protected against thermal effects using the adiabatic, now for short circuit time needs to be limited to ensure limiting temp of cable is not exceeded.

Now for a earth fault current there are two requirements, first we have ADS so disconnection times need to be met, secondly we again need to ensure that the adiabatic equation is met. Alternatively you may use table 54.7(but note second paragraph 543.1.1)
 

Reply to disconnection times in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top