Hello to all,
Have just completed an EICR for a client of mine who would now like me to do the remedial work. I've hit a problem with the design of the job.
Part of the work will involve a new CU with RCDs and possibly a couple of RCBOs
The CU is remote from the meter position and is fed via a 16mm Twin & earth sub main that comes from the meter cabinet via an old 500mA RCD (which does not operate by the way). Now, it is likely that this 16mm T & E runs in partitions within 50mm of the surface and as such should have a 30mA RCD(522.6.202).
Trouble is if I protect the sub main cable with 30mA and have further RCDs in the CU I'm not going to have any discrimination between RCDs, resulting in inconvenience in event of a fault.
Have been thinking of protecting the sub main with a 100mA S type RCD to provide discrimination and some protection too but this is still a departure. Have asked NIC tech help who say I need to ensure reg 120.3 when claiming any departures. Which I don't think I will be with a 100mAmp RCD on the front end.
Any thoughts or help on this will be gratefully received.
Thanks for reading.
Have just completed an EICR for a client of mine who would now like me to do the remedial work. I've hit a problem with the design of the job.
Part of the work will involve a new CU with RCDs and possibly a couple of RCBOs
The CU is remote from the meter position and is fed via a 16mm Twin & earth sub main that comes from the meter cabinet via an old 500mA RCD (which does not operate by the way). Now, it is likely that this 16mm T & E runs in partitions within 50mm of the surface and as such should have a 30mA RCD(522.6.202).
Trouble is if I protect the sub main cable with 30mA and have further RCDs in the CU I'm not going to have any discrimination between RCDs, resulting in inconvenience in event of a fault.
Have been thinking of protecting the sub main with a 100mA S type RCD to provide discrimination and some protection too but this is still a departure. Have asked NIC tech help who say I need to ensure reg 120.3 when claiming any departures. Which I don't think I will be with a 100mAmp RCD on the front end.
Any thoughts or help on this will be gratefully received.
Thanks for reading.