Joined
Jan 13, 2010
Messages
231
Reaction score
56
Hello to all,

Have just completed an EICR for a client of mine who would now like me to do the remedial work. I've hit a problem with the design of the job.

Part of the work will involve a new CU with RCDs and possibly a couple of RCBOs

The CU is remote from the meter position and is fed via a 16mm Twin & earth sub main that comes from the meter cabinet via an old 500mA RCD (which does not operate by the way). Now, it is likely that this 16mm T & E runs in partitions within 50mm of the surface and as such should have a 30mA RCD(522.6.202).

Trouble is if I protect the sub main cable with 30mA and have further RCDs in the CU I'm not going to have any discrimination between RCDs, resulting in inconvenience in event of a fault.

Have been thinking of protecting the sub main with a 100mA S type RCD to provide discrimination and some protection too but this is still a departure. Have asked NIC tech help who say I need to ensure reg 120.3 when claiming any departures. Which I don't think I will be with a 100mAmp RCD on the front end.

Any thoughts or help on this will be gratefully received.
Thanks for reading.
 
Thanks to everyone who replied yesterday.

Quick Update: Spoke to NIC tech help today. The chap I spoke to suggested that I protect the sub main cable with a time delay 100mA RCD in order to maintain discrimination with the downstream RCDs. But that this is a departure and must be noted as such. Also, that it would be a good idea to provide a risk assessment to identify the risk of the potentially buried cable without a 30mAmp (additional protection).

Also to note within the risk assessment that I am in fact improving the overall safety of the installation and not making it less safe than it already is.

Will update again once I've spoken to client

Cheers again
 
It is an interesting choice for the NICEEIC to make, the regulations specifically state that any departure from the regulations, that may be noted on the electrical installation certificate, may not provide any less safety than that provided by compliance with the regulations.
This is not the case in this instance and should not be considered to be complying with the regulations or as an acceptable departure.

However in practical terms increasing the safety of the installation is of benefit and it could be considered that increasing the safety could be undertaken even in contravention of the regulations as otherwise you are retaining a more dangerous state. But that is a decision for the electrician on site to make as a call on a case by case basis.
 

Reply to discrimination conundrum in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
838
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
626

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top