I wonder if someone can answer a question for me . We have to install a new dis-board in a property that already has a landlords distribution equipment installed . The landlords distribution equipment has its own service head and earthing arrangement . We wish to install a new supply taken from the tenets LV system which has its own service head and earthing arrangement some 45m away . The two systems will be sitting side by side . Do we need to ensure a distance because of the two different earthing arrangements ?
 
Speak to the DNO it is for them to specify. Most do not like secondary supplies to the same room. There is a danger that if the supplies are from separate transformers you could get circulating current through the neutrals/earths especially with PME supplies. Another danger is if there is any interconnection between the systems and one transformer is off supply due to a HV fault it would cause a back feed through the interconnection (for a short time anyway)
What you are suggesting is generally a very poor design anyway and trying to do the job on the cheap when you should be getting the correct supply installed.
 

Reply to Distance Between Supplies in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
956

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top