Distance from D/G socket to extended pull out kitchen tap ? Kitchen tap when pulled out is easily with 400 mm of a D/G socket . Not my job . Just asking for clarification etc
 
Don't think there is an actual stated distance in 7671. It would rely on the 'suitable for external influences' test. (Is it likely to be sprayed by the tap, etc).

Lots of bathroom zone pics online that show a zone around the tap but that's not actually based on anything in the Regs

There might be something in other guidance or building Regs...
 
Looks like Guidance Note 1 may say "It is preferable that accessories should not be installed within 300mm of a stainless steel sink unit top"

Though that's again not an absolute requirement...

According to this page, NICEIC guide and NHBC seems to state a minimum distance of 300mm....

Edit: Never seen this document before before, but the NICEIC guide to electrical work in the kitchen says

"Electrical sockets or switches should be fitted at a safe distance (it is recommended at least 30cm horizontally) from a sink to avoid the chance of water coming into contact with electricity."

Electrical Safety First also say:

"To avoid water coming into contact with electricity, make sure that your sockets or switches are fitted at a safe distance (at least 30cm horizontally) from the sink."

so looks like 300mm is guidance, but a good rule of thumb...
 
Its 450mm from the kitchen tap .But once that pull out spout section is extended . The spout can reach to 30mm from the socket .
 
Its 450mm from the kitchen tap .But once that pull out spout section is extended . The spout can reach to 30mm from the socket .
You can't design for what some idiot customer might do. If they're daft enough to spray water on a socket then they may be just as likely to pour a jug of water onto a socket. Or let the steam from a kettle spout be directed onto a socket.

The actual recommended distance of 300mm is horizontally from the edge of the sink/drainer.
 

Reply to DISTANCE from D/G socket to max reach of pull out kitchen tap ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top