D

dean7828

Hi guys can you clear something up for me, if an electrician was to change a distribution board for say a domestic property what would be the extent of the installation the electrician would be responsible for, some people say as long as you state on the certificates that you have only changed the board then you will not be responsible for the rest of the installation, this seems like a cop out to me as you could be reconnecting circuits that would not comply.
 
I was under the impression that you become resposible for any circuits that you touch. As a CU change would mean you are effectivly changing / touching all circuits. Also before and after the CU change you would need to carryout testing to ensure that all circuits are safe. But I could be wrong?
 
IMO you would not connect circuits that did not comply. an exception is lighting without cpc or 2.5mm ring with 1.0mm cpc. you would , however note this on the EIC . you will have tested all circuits before energising and their condition is on the cert. at the time of testing. bit like an MOT. you can't be held responsible for future failure of smomething you have not installed.
 
as long as you test the circuits, Zs,polarity, IR, your cert. shows that the circuits are healthy at the time of testing. you cannot be held responsible for future events, e.g. DIY man adds an extra socket and gets it wrong.
 
As you would be changing the characteristics of every circuit fed by the DB, you would be required to generate a full installation certificate, therefore the responsibility would ultimately be yours as you are signing the test certificate. Obviously any departures from BS7671 would be noted on the test sheets, as well as agreed limitations (hell we can't see through walls to say circuits are within prescribed zones!!)
 
No, you do not become responsible for the existing installation when changing a DB.
You are required to ascertain before making any addition or alteration, that the rating and condition of the existing equipment that shall remain after the addition or alteration will be adequate.
Being adequate, does not neccessarily mean that such equipment must comply with BS7671.

The details of the addition or alteration should be described on the certificate, and any departures should be noted.
The designer is required to attest that any departures shall provide the same degree of safety as would be obtained by compliance with the Regulations.

During installation, and upon completion of the addition or alteration, appropriate inspection and testing shall be conducted and the results if any should be noted on the respective inspection and test schedules. Any and all defects in the work to install the addition or alteration as detailed on the certificate should be rectified before issuing the certificate. Any defects in the existing installation should where reasonably practicable be noted on the certificate.
There is no provision for limitations when issuing a certificate.
 
Last edited by a moderator:

Reply to Distribution board change responsibilities in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
664
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I tend to write the circuit number on the mcb say every 5th mcb/rcbo just to help make it easier to locate in a large multi way or 3ph board...
2
Replies
17
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top