Hi all, quite new to this forums so hopefully this is in the right place.

I have a combi boiler, please see picture of the old wiring of the thermostat and how I have wired up the new smart thermostat. Boiler still comes on but no display to the thermostat. Also I tried 4 into 1 but still no luck. If anyone could advise please? 1000002390.jpg1000002531.jpg
 
Do you have 230v between terminals 3 and 4?
If not then how about 2 and 3?
 
If you have 230v between 3 and 4 then the unit is faulty if it won’t light up.
 
Hi all, quite new to this forums so hopefully this is in the right place.

I have a combi boiler, please see picture of the old wiring of the thermostat and how I have wired up the new smart thermostat. Boiler still comes on but no display to the thermostat. Also I tried 4 into 1 but still no luck. If anyone could advise please? View attachment 119062View attachment 119063
Looks exactly like mine ,I bought it off amazon ,was a nightmare to program ,soft ware was rubbish so we just set it to 20 degrees during day and get off our backsides at night to turn it up.if I remember right the app is called becca smart.no wonder our gas bill is thru the roof
 
Last year I removed six 'stats from one of my holiday cottages, that looked similar, from the back at least, to the OP's new ones and replaced them with ones that had internals similar to the OP's original.
Became fed up with guests messing with the (incomprehensible) programming, so now just simple rotary dials with limit stops.
 
Last year I removed six 'stats from one of my holiday cottages, that looked similar, from the back at least, to the OP's new ones and replaced them with ones that had internals similar to the OP's original.
Became fed up with guests messing with the (incomprehensible) programming, so now just simple rotary dials with limit stops.
Hive must be making a fortune cos the amount of customers buying them on the black Friday sale was ridiculous. I must have connected up 5 since September and the plumber I work with seems to only supply hive .I prefer nest its sleeker comes in different colours and just feels better.only problem is the charging wire .fine if you have an old stat but most don't so opt for the stand .the reciever is better as well with cable clamps .
 
Hi all, quite new to this forums so hopefully this is in the right place.

I have a combi boiler, please see picture of the old wiring of the thermostat and how I have wired up the new smart thermostat. Boiler still comes on but no display to the thermostat. Also I tried 4 into 1 but still no luck. If anyone could advise
Hi all, quite new to this forums so hopefully this is in the right place.

I have a combi boiler, please see picture of the old wiring of the thermostat and how I have wired up the new smart thermostat. Boiler still comes on but no display to the thermostat. Also I tried 4 into 1 but still no luck. If anyone could advise please? View attachment 119062View attachment 119063
Some of these stats have factory resets you could Google it rather than splash out .Worth a try
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
North Yorkshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Old thermostat to smart thermostat wiring issue
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
TheeMarko,
Last reply from
Jock from the north,
Replies
7
Views
504

Advert

Back
Top