Not sure how tight it was - e.g. could the DB cover be opened ? - this will need 1/2 mtre at least , some DBs are much bigger so depends really, then is the door hinge the right side so you can actually get at it.
This is for the purpose of isolation, never mide working on the board.
BS7671 covers this and although not dimensioned, it has to be accessible. I have come across DBs that you simply cannot get at for plant and machinery so i assume nothing about the situation you have come across.
Now if you were going to work on it, that is another matter. You need to be able to totally remove the cover which is screwed on, this usually mean the door has to be fully open to remove the screws. Then you need room to work........ Accessable to me is a minimum of 1M probably more like 1.5-2.
FWIW i code installations i come across with inadequate access when i carry out inspections to BS7671
This is for the purpose of isolation, never mide working on the board.
BS7671 covers this and although not dimensioned, it has to be accessible. I have come across DBs that you simply cannot get at for plant and machinery so i assume nothing about the situation you have come across.
Now if you were going to work on it, that is another matter. You need to be able to totally remove the cover which is screwed on, this usually mean the door has to be fully open to remove the screws. Then you need room to work........ Accessable to me is a minimum of 1M probably more like 1.5-2.
FWIW i code installations i come across with inadequate access when i carry out inspections to BS7671