Is this actually a job or a 'hypothetical' question? Because if its a job you really-really want to make sure you get it right. Could be a VERY expensive mistake if you are relying on forum answers to very poorly phrased questions.
 
Just because you have a free 160A doesn’t mean it has to be used to capacity. If it’s a switch fuse, fit smaller fuses, a MCCB, change the MCCB.

This may sound ridiculous I found a board fed with a 25mm² 4c SWA. The nearest free distribution switch fuse was 800A. They left the 800A fuses in because that was what was fitted.

Work out your existing plus anticipated loading and then determine the OCPD. Don’t try to work the other way around.
 
I completed my electrical apprentership but changed jobs to cable jointing. If the cable your talking about is coming out of a substation its either PILC or waveform and if you clean the cable back around 2meters it will state the size. Also if your changing lights to LED's your max load will decrease so why are you upgrading to a 3phase supply ? your load will dercrese
 

Reply to Distribution board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
664
  • Question
Useful to know. In my case there will be 150x150mm trunking at top/bottom and almost certainly I will be using tri-rated cable, probably 70mm...
Replies
4
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top