On the EIC page 3 it says to record details of these on first line, would that just be on the circuit details side of the form? or do you have to fill in test results for tails too?
 
amberleaf
Respected Member


Join Date: Mar 2009
Posts: 1,046
Thanks: 0
Thanked 486 Times in 348 Posts
Re: Section - 301- Questions - Testing ,
Recording of Circuit details and Test Results for Distribution Circuits :

Regulation 514.9.1 and Chapter 63 ( Certification & Reporting ) call for circuit details and test results to be provided for all circuits in an Electrical Installation , However, there is sometimes a tendency to Overlook the provision of this information for Distribution Circuits ( or Sub-Mains as they are sometime called ) where such circuits form part of the installation . the requirement to provide such information applies to Distribution Circuits as it does to final circuits .

One Situation where this type of Omission of Data Occurs is where a Main Switch , located at the Origin , feeds a Single Distribution Circuit to a Remote Distribution Board or Consumer Unit . ► Without this Recorded Data the Certification for the Installation is Incomplete .
This does Not Apply to Meter Tails making the Short Connection between the Consumer Unit or Main Switch to the Electricity Meter or Distributor’s Isolator .

Example of a Distribution Circuit :-
Electricity Distributor’s Overload Protective Device ,
Meter Tails ,
~ Main / Switch – Switch / Fuse ,
SWA – cable ( Distribution Circuit ) ,
~ Remote Consumer Unit , ◄




Thanks amberleaf;)
 

Reply to distribution circuit at origin (meter tails) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
800

Similar threads

yeah so it looks like an old off peak heating circuit to what would have been storage heaters my preference is to remove them completely from the...
Replies
2
Views
274
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top